    Sep 2022
    uk
    13
    Mitsubish city multi - not heating
    I have an issue with a Mitsubishi city multi system not providing much heat.
    system is circa 2001 - but still in reasonable condition. Outdoor is a PURY P250 YMF with 9 ducted PDYF P20 indoor units. I suspected it may have been short of gas - but recovered and gas charge - is as per commissioning sheet.
    Hot gas seems to reaching the BC box(49c) - but air off temp at indoors is only around 22c
    I got the following data from sw1
    Comp freq 82
    Discharge 20 bar
    Suction 3 bar
    BC box P1 47 P3 39
    TH11 10.3
    TH12 1.7
    TH13 99?
    TH14 99?
    TH15 0
    TH16 12.8
    LEV 3 440
    INDOOR LEV'S - ALL AT 2000
    Any ideas?
    ireland
    1,451
    Re: Mitsubish city multi - not heating
    What are your actual suction and discharge pressures? Do they correspond to what the system thinks the pressure transducers are reading?
    Sep 2022
    uk
    13
    Yes - gauges read the same as sw1 readings
    ireland
    1,451
    Is it 407c? What discharge temp are you getting? Is compressor at full speed for above readings?
    Sep 2022
    uk
    13
    Yes it’s a 407c unit. I spent a bit of time looking at it today.one thing I found - was that th1 thermistor{ compressor discharge) was reading 123c even with the unit off, I changed the sensor but it made no difference, still showed 123c when running, when-pipe temp was only 76c.
    Would this be enough, to stop the compressor ramping up to full load ? Im presuming it must be an issue with the main board causing the sensor reading error.
    I have a board off a PUHY YMF C, it looks the same, but was going to check to see if it’s compatible with a PURY unit, as a replacement board is £350 .
    ireland
    1,451
    Yes, i think this will prevent full load on compressor, big weird that just this thermistor is not reading right, worth checking board though.
    Aug 2007
    Russia
    139
    22
    If this is a PURY-P250 YMF-C unit than the discharge temp. probe is TH11 and not TH1.
    Sep 2022
    uk
    13
    Hi Narkom, thanks for your reply.
    yes its a PURY - P250 YMFC CIRCA 2001
    My manual doesn't list any SW1 switch settings for a th 11 - do you have them
    thanks
    Aug 2007
    Russia
    139
    22
    This is the manual for a PURY-200YMF unit and not for PURY-P200YMF.
    I have a manual for PURY-P400, 500YMF-C, hope this will help
    https://www.mediafire.com/file/ijbxyd1se1zevb5/F1105_214.pdf/file