    Capacity calculation

    How do I calculate the needed capacity to cool 5000 kg/h vegetables in a cooling tunnel from 20°C to 1°C with a time in the tunnel of 6 minutes?
    5000 kg/hx 0.8 cal/kg°C x 19Kbut what about the latent heat?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Capacity calculation

    5000kg/h = 500kg per 6 minutes so your calc should be for 500kg (the actual load in the tunnel at any one time.

    The latent process can be ignored as you are not going below freezing (phase change)

    So, your calc should be
    Q = m x C x dT all divided by the time is seconds and chilling factor.
    What vegetables are they Peter?

  3. #3
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Capacity calculation

    Quote Originally Posted by Peter_1
    How do I calculate the needed capacity to cool 5000 kg/h vegetables in a cooling tunnel from 20°C to 1°C with a time in the tunnel of 6 minutes?
    5000 kg/hx 0.8 cal/kg°C x 19Kbut what about the latent heat?
    Peter I make it 104kW including 10% fan load. thats taking the product specific heat capacity of 3.7 kJ/kG

    No allowance for air change or infiltration in that.

    Probably a 125kW tunnel and plant, giving a good safety factor

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Capacity calculation

    I explained/translated it the wrong way I see now.
    It should have been respiration heat, due to the fact that vegetables are a living metabolism and produce heat, other then meat.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Capacity calculation

    Quote Originally Posted by Peter_1
    I explained/translated it the wrong way I see now.
    It should have been respiration heat, due to the fact that vegetables are a living metabolism and produce heat, other then meat.
    I don't think you did Peter. Specific heat Capacity before freezing is just the same for meat or vegetables.

    Have a revision look in Dossat.

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Capacity calculation

    Using a chilling factor of 0.85 I get 114.8KW. Add to that a safety factor and I agree with Andy's suggestion of 125kw.

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Capacity calculation

    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,261
    Rep Power
    31

    Re: Capacity calculation

    Hi, Peter_1

    Quote Originally Posted by Peter_1
    I explained/translated it the wrong way I see now.
    It should have been respiration heat, due to the fact that vegetables are a living metabolism and produce heat, other then meat.
    See attachment,

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  9. #9
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Capacity calculation

    Thanks all,

    I need to use figures which are correct.
    It's for the case with the potatoes cooling tunnel.

    I had a small problem with the HD in my head

    I had a table which gave BTU/lb and thought there was something wrong with it and I see now that should have been BTU/lb/hour.

    Is following calculation then correct if I count the load per hour
    5.000 kg/hour (11.023 lb/hour) entering at 20°C (68°F) and leaving at 1°C (33.8°F), specific heat of 0.8 and a respiration heat of 0.028 kcal/kg°C (or 0.028 BTU/lb/hour)
    gives (5000 x (20-19) x 0.8) + (5000 x 0.028 x 19) = 76.000 kcal + 2.660 kcal = 78.660 kcal or 91 kW + eventually additional load like Andy said for the fans but the motor of the fans are outside the tunnel and the fanblade itselves is connected to the inside via a long shaft/rod on the motor.

    Or (11.023 x (68-33.8) x 0.8 ) + (5000 x (68-33.8) x 0.028 = 301589 + 10555 = 312144 BTU/hour)
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  10. #10
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,261
    Rep Power
    31

    Re: Capacity calculation

    Hi, Peter_1

    Are you sure you can cool 5000 kg of potato from 20C down to 1C in one hour

    Maybe I miss something

    http://www.uidaho.edu/ag/plantdisease/pstore.htm

    http://www.uidaho.edu/ag/plantdiseas...re.htm#anchor4

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  11. #11
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Capacity calculation

    Corrected givest his:

    5.000 kg/hour (11.023 lb/hour) entering at 20°C (68°F) and leaving at 1°C (33.8°F), specific heat of 0.8 and a respiration heat of 0.028 kcal/kg°C (or 0.028 BTU/lb/hour)
    gives (5000 x (20-19) x 0.8) + (5000 x 0.028) = 76.000 kcal + 140 kcal = 76.140 or 88.5 kW + eventually additional load like Andy said for the fans but the motor of the fans are outside the tunnel and the fanblade itselves is connected to the inside via a long shaft/rod on the motor.

    Or (11.023 x (68-33.8) x 0.8 ) + (11.023 x 0.028) = 301589 + 309 = 301897 BTU/hour

    Im' busy with the report this Sunday. Already 35 pages.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. R-407C and Coil Capacity
    By glabah in forum Refrigerants
    Replies: 5
    Last Post: 03-06-2006, 11:36 AM
  2. Capacity achievement
    By Hemant Anand in forum Industrial
    Replies: 8
    Last Post: 18-12-2005, 01:18 AM
  3. New Capacity Control Solution
    By embrown in forum New Technologies
    Replies: 19
    Last Post: 30-12-2003, 01:33 PM
  4. TEV capacity related to pressure drop
    By DaBit in forum CPU Overclockers
    Replies: 8
    Last Post: 06-12-2002, 05:11 PM
  5. Relative Power / Capacity data
    By Argus in forum Air Conditioning
    Replies: 3
    Last Post: 01-08-2002, 09:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •