    Capacity calculation



    How do I calculate the needed capacity to cool 5000 kg/h vegetables in a cooling tunnel from 20°C to 1°C with a time in the tunnel of 6 minutes?
    5000 kg/hx 0.8 cal/kg°C x 19Kbut what about the latent heat?


    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Capacity calculation

    5000kg/h = 500kg per 6 minutes so your calc should be for 500kg (the actual load in the tunnel at any one time.

    The latent process can be ignored as you are not going below freezing (phase change)

    So, your calc should be
    Q = m x C x dT all divided by the time is seconds and chilling factor.
    What vegetables are they Peter?

  3. #3
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Capacity calculation

    Quote Originally Posted by Peter_1
    How do I calculate the needed capacity to cool 5000 kg/h vegetables in a cooling tunnel from 20°C to 1°C with a time in the tunnel of 6 minutes?
    5000 kg/hx 0.8 cal/kg°C x 19Kbut what about the latent heat?
    Peter I make it 104kW including 10% fan load. thats taking the product specific heat capacity of 3.7 kJ/kG

    No allowance for air change or infiltration in that.

    Probably a 125kW tunnel and plant, giving a good safety factor

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Capacity calculation

    I explained/translated it the wrong way I see now.
    It should have been respiration heat, due to the fact that vegetables are a living metabolism and produce heat, other then meat.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Capacity calculation

    Quote Originally Posted by Peter_1
    I explained/translated it the wrong way I see now.
    It should have been respiration heat, due to the fact that vegetables are a living metabolism and produce heat, other then meat.
    I don't think you did Peter. Specific heat Capacity before freezing is just the same for meat or vegetables.

    Have a revision look in Dossat.

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Capacity calculation

    Using a chilling factor of 0.85 I get 114.8KW. Add to that a safety factor and I agree with Andy's suggestion of 125kw.

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Capacity calculation

    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Capacity calculation

    Thats alright but you are talking about 6 MINUTES so I think you can ignore it

    the following was taken from your link

    he longer the time required to cool the produce, the greater the total respiration heat.

  9. #9
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Capacity calculation

    Hi, Peter_1

    Quote Originally Posted by Peter_1
    I explained/translated it the wrong way I see now.
    It should have been respiration heat, due to the fact that vegetables are a living metabolism and produce heat, other then meat.
    See attachment,

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Capacity calculation

    Thanks all,

    I need to use figures which are correct.
    It's for the case with the potatoes cooling tunnel.

    I had a small problem with the HD in my head

    I had a table which gave BTU/lb and thought there was something wrong with it and I see now that should have been BTU/lb/hour.

    Is following calculation then correct if I count the load per hour
    5.000 kg/hour (11.023 lb/hour) entering at 20°C (68°F) and leaving at 1°C (33.8°F), specific heat of 0.8 and a respiration heat of 0.028 kcal/kg°C (or 0.028 BTU/lb/hour)
    gives (5000 x (20-19) x 0.8) + (5000 x 0.028 x 19) = 76.000 kcal + 2.660 kcal = 78.660 kcal or 91 kW + eventually additional load like Andy said for the fans but the motor of the fans are outside the tunnel and the fanblade itselves is connected to the inside via a long shaft/rod on the motor.

    Or (11.023 x (68-33.8) x 0.8 ) + (5000 x (68-33.8) x 0.028 = 301589 + 10555 = 312144 BTU/hour)
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Capacity calculation

    Hi, Peter_1

    Are you sure you can cool 5000 kg of potato from 20C down to 1C in one hour

    Maybe I miss something

    http://www.uidaho.edu/ag/plantdisease/pstore.htm

    http://www.uidaho.edu/ag/plantdiseas...re.htm#anchor4

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  12. #12
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Capacity calculation

    It are in fact fresh French Fries, at a rate of 5.000 kg/u. Tehy have to be cooled down to 1°C before packing.
    It's a coninue line from raw potatoes till packed FF.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  13. #13
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Capacity calculation

    Hi, Peter_1

    Quote Originally Posted by Peter_1
    It are in fact fresh French Fries, at a rate of 5.000 kg/u. Tehy have to be cooled down to 1°C before packing.
    It's a coninue line from raw potatoes till packed FF.
    It is clear now

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  14. #14
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Capacity calculation

    Peter,

    You were asking for some comments on the load calculations. I see you are still working on the french fry cooling tunnel problem.

    ...for the fans but the motor of the fans are outside the tunnel and the fan blade itselves is connected to the inside via a long shaft/rod on the motor.
    It does not matter if the fan motors are external to the tunnel. The motors are still adding energy to the air (and load) inside the tunnel.

    The fan motors will have some inefficiency, this is the heat that is produced by the motor. Since this is external to the tunnel this heat does not become part of the refrigeration load. This is normally about 15-20% for small motors.

    The remaining energy is used to turn the fan blades. Since the fan blades are inside of the cooling tunnel, the majority of the energy used by the motors is absorbed by the air.

    Does this cooling tunnel also have an exhaust fan to remove the CO2 or nitrogen ( I forgot which one you were using) from the tunnel. The volume of air this fan moves could also be considered part of the cooling load (at least as far as the cyrogen is considered).

    You will also have some air cooling load that enters the tunnel. This might be part of the exhaust fan volume flow, I'm not sure what you have.

    Also, the respiration heat is based on Energy/Mass-Time. So in IP units, you are looking at Btu/pound-time (the time rate could be minutes, hours, or 24 hours).

    In your calculation you show:
    (11.023 x (68-33.8) x 0.8 ) + (5000 x (68-33.8) x 0.028 = 301589 + 10555 = 312144 BTU/hour)
    The 5000 shown in red should be 11.023 (lb/hour). However, the respiration heat should not include the dT for the product.

    If the respiration heat is 0.028 Btu/lb-hr, then you should be multiplying 11.023 pounds X 0.028 Btu/pound-hr to get 308.6 Btu/hr. The pounds(mass) cancel out each other, so you are left Btu/hr.

    If you multiple 11.023 pounds per hour X 0.028 Btu/pound-hr X dT the units get scrambled up into something that does not makes sense. (Btu-F/hr)

    Does that help?
    Last edited by US Iceman; 02-07-2006 at 11:19 PM.

  15. #15
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Capacity calculation

    Corrected givest his:

    5.000 kg/hour (11.023 lb/hour) entering at 20°C (68°F) and leaving at 1°C (33.8°F), specific heat of 0.8 and a respiration heat of 0.028 kcal/kg°C (or 0.028 BTU/lb/hour)
    gives (5000 x (20-19) x 0.8) + (5000 x 0.028) = 76.000 kcal + 140 kcal = 76.140 or 88.5 kW + eventually additional load like Andy said for the fans but the motor of the fans are outside the tunnel and the fanblade itselves is connected to the inside via a long shaft/rod on the motor.

    Or (11.023 x (68-33.8) x 0.8 ) + (11.023 x 0.028) = 301589 + 309 = 301897 BTU/hour

    Im' busy with the report this Sunday. Already 35 pages.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  16. #16
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Capacity calculation

    Hi Peter,

    The last post you made I agree with. You should also add any additional motor power input to the load calc.'s, i.e., conveyor, etc.

    Good luck with the report.

Similar Threads

  1. R-407C and Coil Capacity
    By glabah in forum Refrigerants
    Replies: 5
    Last Post: 03-06-2006, 11:36 AM
  2. Capacity achievement
    By Hemant Anand in forum Industrial
    Replies: 8
    Last Post: 18-12-2005, 01:18 AM
  3. New Capacity Control Solution
    By embrown in forum New Technologies
    Replies: 19
    Last Post: 30-12-2003, 01:33 PM
  4. TEV capacity related to pressure drop
    By DaBit in forum CPU Overclockers
    Replies: 8
    Last Post: 06-12-2002, 05:11 PM
  5. Relative Power / Capacity data
    By Argus in forum Air Conditioning
    Replies: 3
    Last Post: 01-08-2002, 09:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •