    Cool Daikin VRVII loading problem



    I have a situation where there is an REYQ46 installed and there is one zone which is a 125 fcu which is on the west zone which has a high solar load. My problem is when all other zones are satisfied and this is the only zone calling for cooling the condensing set does not respond. It only ramps up when I turn other fcu set temps down to give it load does it respond. Any ideas??



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Daikin VRVII loading problem

    Does the affected unit cool if the rest of the system is running?
    Is this a new install or an existing one with a new fault?

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin VRVII loading problem

    Does the outdoor unit 'see' this fan coil. Have you done a fan coil count on the outdoor pcb?

  4. #4
    Leigh's Avatar
    Leigh Guest

    Re: Daikin VRVII loading problem

    the fcu inquestiondoes function correctly when other fcus are running. Problem seems to be when calling for cooling on its own. It is registering at the outdoor unit

  5. #5
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Daikin VRVII loading problem

    i think it is set up as a slave unit!
    is that you coffill?
    with your tryhard mo?

    Quote Originally Posted by Leigh View Post
    I have a situation where there is an REYQ46 installed and there is one zone which is a 125 fcu which is on the west zone which has a high solar load. My problem is when all other zones are satisfied and this is the only zone calling for cooling the condensing set does not respond. It only ramps up when I turn other fcu set temps down to give it load does it respond. Any ideas??

  6. #6
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Daikin VRVII loading problem

    i bet both units are on the same bs unit!


    Quote Originally Posted by Leigh View Post
    the fcu inquestiondoes function correctly when other fcus are running. Problem seems to be when calling for cooling on its own. It is registering at the outdoor unit

  7. #7
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Daikin VRVII loading problem

    do you have local remotes,? as they may be swapped or on the i touch that unit maybe registered as a slave unit and only does what the other units do on the system and follow suit..


    Quote Originally Posted by brunstar View Post
    i think it is set up as a slave unit!
    is that you coffill?
    with your tryhard mo?

Similar Threads

  1. Problem with an inverter compressor in V.R.V system DAIKIN R 407
    By Harris Greece in forum Air Conditioning
    Replies: 10
    Last Post: 24-11-2007, 12:53 AM
  2. Problem with ducted Daikin
    By jutty in forum Trouble Shooting
    Replies: 8
    Last Post: 23-07-2007, 05:34 AM
  3. !!big Daikin Problem!! Codes,u4,pj, And E0
    By airconengineer in forum Air Conditioning
    Replies: 21
    Last Post: 31-05-2007, 09:04 PM
  4. Daikin problem
    By Jambo in forum Trouble Shooting
    Replies: 4
    Last Post: 28-07-2006, 07:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •