Thread: Daikin VRVII loading problem
-
26-09-2007, 12:40 PM #1
Daikin VRVII loading problem
I have a situation where there is an REYQ46 installed and there is one zone which is a 125 fcu which is on the west zone which has a high solar load. My problem is when all other zones are satisfied and this is the only zone calling for cooling the condensing set does not respond. It only ramps up when I turn other fcu set temps down to give it load does it respond. Any ideas??
-
26-09-2007, 05:27 PM #2
Re: Daikin VRVII loading problem
Does the affected unit cool if the rest of the system is running?
Is this a new install or an existing one with a new fault?
-
26-09-2007, 08:09 PM #3
Re: Daikin VRVII loading problem
Does the outdoor unit 'see' this fan coil. Have you done a fan coil count on the outdoor pcb?
-
01-10-2007, 01:27 PM #4
Re: Daikin VRVII loading problem
the fcu inquestiondoes function correctly when other fcus are running. Problem seems to be when calling for cooling on its own. It is registering at the outdoor unit
-
24-11-2007, 12:52 AM #5
-
24-11-2007, 12:56 AM #6
-
24-11-2007, 02:35 PM #7