    Oct 2005
    IRAN
    878
    Superheat reference
    Hi there,
    A normal superheat at the evaporator outlet should be between 5 to 10K. Lower than 5K would result in liquid flood-back and higher value will overload the compressor and lowers the refrigeration capacity.
    I need a reliable reference for these values. I searched ASHRAE and many other references but not luck.
    Does anyone know a reference?
    Appreciate your help.
    Even Einstein Asked Questions
    3,355
    Re: Superheat reference
    Lana,
    Please find some links, hopefully useful, but somehow think not.
    Can depend on what type of TX valve, as electronic very accurate.
    Also could not find article about superheat cannot be higher at evaporator outlet than air on temperature/ SST
    https://www.parker.com/literature/Af...V%20Theory.pdf
    https://www.coolconcerns.co.uk/image...EV_setting.pdf
    Feb 2011
    scotland
    452
    What about using the compressor manufactures technical info for the particular compressor being used?
    Oct 2005
    IRAN
    878
    Thanks for the replies.
    I don't have a problem in keeping the superheat in a normal range. For some refrigerants like R290 we need at least 20K and ....
    I just need a reference where this range is mentioned.
    Thanks again.
    3,355
    Wrong location