    Question Need wiring diagrams for grasso kab monitron CR
    Hello my friends
    I want the wiring diagram for unit screw that controlled with MONITRON CR grasso KAB.
    The product date of this unit 1996 and screw compressor model is G-2.
    Please help me.
    Thank you very much.
    Best regards.
  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46
    Re: Need wiring diagrams for grasso kab monitron CR
    Quote Originally Posted by MarcoPatriot View Post
    Hello my friends
    Please help me.
    Best regards.
    Hi Marco.
    Please use the attached link which should allow you to access / download the appropriate attached Manual.
    Regards Grizzly
    https://www.mediafire.com/file/2uggu...-en-0089243.pd
    Despite the High Cost of Living it still remains Popular!
  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46
    Just to add Marco. Myself and My friend and Ex colleague Paul. Successfully converted a Grasso rig of the same configuration as your to a Sabroe Unisab Control system.
    Which was a blast Spiral freeze system on Ammonia. That was 2016 and is still to my knowledge still successfully running today.
    We / the customer had re-occuring issues with the Monitron which was becoming more and more unstable. Hence the retrofit.
    Good luck. Grizzly