    Ascon ac multi split



    having problem with an ascon multi split system. just wondering if any one has worked on these units. i have previously fitted a multi plits system in the past 2 months . I'm now having problems with the contactor of the compressor chattering. would like to know if any one else has come across an other problems and how they were resolved



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Ascon ac multi split

    A contactor / relay chattering is normally cause by low voltage across the coil. The coil has a threshold below which the coil will not hold 'in'.
    Check you control circuit from start origin and look out for a major volt drop.

  3. #3
    Join Date
    Jun 2006
    Location
    england
    Posts
    25
    Rep Power
    0

    Re: Ascon ac multi split

    May now think that the contactor coil is 400v (across A1 and A2 ). this would link up with what frank has said about the major voltage drop. would this cause the chattering or would the contacor not pull anyway. One thing i have tried that seem to reslove the chattering was to re wire the crank case heater . the crank case heater took its live from an normally closed side of the contactor , (linked across from one of the 3 phase supplies) and ended its neutral on the same pole as the neutral for the signal for the contactor( A2). i rewired the crank case heater directly to the neutral block of the unit. my question is would the normally closed pole of the contactor that feeds the cch interupt the neutral of the contactor coil and cause it to chatter.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Ascon ac multi split

    How can you have a 400v contactor coil if you have neutral on A2?

  5. #5
    Join Date
    Jun 2006
    Location
    england
    Posts
    25
    Rep Power
    0

    Re: Ascon ac multi split

    would it be possible if the manufactuer had put on 400v coil contactor by mistake that this would create the chattering being experience or would the contactor not pull

  6. #6
    Join Date
    Jun 2006
    Location
    england
    Posts
    25
    Rep Power
    0

    Re: Ascon ac multi split

    the contactor not pull in

    sorry

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Ascon ac multi split

    Quote Originally Posted by mike live
    would it be possible if the manufactuer had put on 400v coil contactor by mistake that this would create the chattering being experience or would the contactor not pull
    Quite possibly Mike - has the unit run before or are you trying to commission it?

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Ascon ac multi split

    You don't need to post twice Mike. If you have made a mistake or forgotten to add something then just click on the EDIT button and SAVE the changes

  9. #9
    Join Date
    Jun 2006
    Location
    england
    Posts
    25
    Rep Power
    0

    Re: Ascon ac multi split

    the twin split system has been commission , and is running at present . the only time this system starts to recreate the chattering was when indoor evap (which has different power supply and the control relays for compressor, condersor fan motor and 4 way valve) was turned on befor the condensing unit. cheers frank just done that edit thing
    Last edited by mike live; 29-06-2006 at 09:00 PM.

  10. #10
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Ascon ac multi split

    Are the indoor and outdoor units fed from the same phase?

    There could be some interference getting to the control circuit.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  11. #11
    Join Date
    Jun 2006
    Location
    england
    Posts
    25
    Rep Power
    0

    Re: Ascon ac multi split

    not too sure . there is a three phase supply coming from one dis board for the power supply to the condensors, and a ring supply for the evaps coming off a different board . they had to be different boards as the supply to any equipment inside the buiulding had to go through a fire managment system.

    if there was a difference in which phase was used for the contactor signal, in what way could this disturb the 240v signal.

    The ascon unit has a 3 core interconect ( plus an earth ) that controls the operation of out door fan, 4 way valve and compressor . this 240 signal comes from indoor pc.

    just found a modification diagram for a multi system will try to attach
    Last edited by mike live; 29-06-2006 at 11:15 PM.

  12. #12
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    62
    Posts
    588
    Rep Power
    19

    Re: Ascon ac multi split

    I have had equipment fed from different boards before and it does cause problems, we discussed it at night school many years ago when I did my then 15th edition and there was a reason behind it that I can not remember. I think a long term solution would be to run off the same board and not mix supplies.

  13. #13
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Ascon ac multi split

    But did you check the voltages with a meter?

  14. #14
    Join Date
    Feb 2005
    Location
    Aberdeen
    Age
    48
    Posts
    168
    Rep Power
    20

    Re: Ascon ac multi split

    Check all electrical wiring for tightness.
    Could possibly be loose wiring causing problem.

    Jase

  15. #15
    Join Date
    Jun 2006
    Location
    england
    Posts
    25
    Rep Power
    0

    Re: Ascon ac multi split

    I have checked all wiring . does not seem to be a problem there . would also like to note that this has not justed happed to one unit . At least 2 more twin split systems have had this problem (2 units myself and a third with a different engineer) problem was iether resloved by disconnecting the neutral for the cch and turning power supply for the condersor befor the evap. will probably need to attach wiring diagrams so you can see what i'm working on . next time go to job will take photo evidence

Similar Threads

  1. Daikin Multi Split A/C problems
    By timholmes204 in forum Air Conditioning
    Replies: 6
    Last Post: 22-05-2008, 12:09 AM
  2. ceiling concealed multi split
    By SIRROM in forum Air Conditioning
    Replies: 7
    Last Post: 22-08-2006, 01:47 PM
  3. Split unit (Recommendations)
    By Smokey in forum Air Conditioning
    Replies: 7
    Last Post: 26-07-2006, 10:04 PM
  4. Need input on City Multi
    By TDfromNY in forum Air Conditioning
    Replies: 4
    Last Post: 09-06-2006, 03:31 AM
  5. Replies: 8
    Last Post: 20-05-2006, 04:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •