    bev air problems. Help



    Recently just replaced A locked compressor in a bevereage air prep table. sp60-16. 134a. New drier. Evacuated and recharged. Problem is high side pressure is near 170 and low near vacum and would stay there after startup. So i replaced the cap tube thinking there may be a restriction, same problem low side is slightly higher. And box temp won't budge below 49deg Any ideas on something i may be missing, or where I can get a perfoemance chart for this unit. Thanks for any help you can give.



  2. #2
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: bev air problems. Help

    Turn it off and see how fast it equaizies it should be less then 4 minutes, If longer you may have a restrictionin liquid line/cap tube/strainer

  3. #3
    Join Date
    Jun 2006
    Location
    ct
    Age
    44
    Posts
    10
    Rep Power
    0

    Re: bev air problems. Help

    Pressure equilizes pretty quickly, Plus the drier and cap tube are new. Also I check for restirictions while the compressor was out. It was about 82Deg with somewhat high humidity. The evaporator was icing up at the inlet so I added alittle more gas. pressures are now 10 and 185. this seems kind of high to me, especially because it;s not cooling as it should.

  4. #4
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: bev air problems. Help

    Go to 20# on the low side

  5. #5
    Join Date
    Jun 2006
    Location
    ct
    Age
    44
    Posts
    10
    Rep Power
    0

    Re: bev air problems. Help

    those pressures don't seem high? I"ll try it and see what hapens. Thanks

  6. #6
    Join Date
    Jun 2006
    Location
    ct
    Age
    44
    Posts
    10
    Rep Power
    0

    Re: bev air problems. Help

    brought the low up to 15 high to 195, seems to be running good.

  7. #7
    Join Date
    Jul 2006
    Location
    USA
    Age
    60
    Posts
    5
    Rep Power
    0

    Re: bev air problems. Help

    I have a similar problem (if it is a problem). I have a Beverage-Air DD58 (Direct Draw Beer Cooler). I just replaced the compressor, and the unit seems to be running well -- cools fine, but the pressures seem wrong. The suction pressure is between 8 and 10 psig; condensing pressure (taken at the end of the condenser) is in the 180 to 190 psig range. Condenser subcooling is around 24 degrees F; suction superheat (measured at the end of the evaporator) is between 17 and 26 degreees F. All of this is in 80-90 degree F ambient.

    The subcooling at the condenser is too high, from what I understand, indicating a possible overcharge, but I'm afraid that if I remove any refrigerant I'll be pulling a vacuum. Any thoughts?

    By reading other threads, I can tell that one of the answers I'll get back is, "If it's cooling properly, you don't have a problem." I'll accept that answer, but I want to be sure I'm not going to damage the new compressor I just put in (or cause any other problem with the unit down the road).

Similar Threads

  1. Replies: 10
    Last Post: 18-03-2006, 07:35 PM
  2. Problems LG don't want you to know about
    By Andy W in forum Air Conditioning
    Replies: 11
    Last Post: 16-02-2006, 04:52 PM
  3. Oil return problems
    By Peter_1 in forum Industrial
    Replies: 37
    Last Post: 23-08-2004, 11:30 PM
  4. oil pressure problems on air dryer
    By edge in forum Trouble Shooting
    Replies: 1
    Last Post: 16-07-2002, 02:10 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •