    low duct temperature



    I have a 2.5 ton split unit. New evaporator last year. It all worked fine until now. However now I cannot get lower than 65 degrees out of the duct anywhere in the house. This was in the 50's before.
    Suction 125
    head 280
    Condenser unit is about 4 years old. Seams to be working good.
    I am at a loss.

    Thanks

    Rick



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: low duct temperature

    Pressures are meaningless without knowing what refrigerant you are talking about.

    Other parameters such as air entering, air leaving, room temp etc. also help.

  3. #3
    Join Date
    Jun 2022
    Location
    USA
    Posts
    2
    Rep Power
    0

    Re: low duct temperature

    Quote Originally Posted by frank View Post
    Pressures are meaningless without knowing what refrigerant you are talking about.

    Other parameters such as air entering, air leaving, room temp etc. also help.
    Sorry r410

    superheat 10-13
    subcooling 10

    air into evaporator 73
    room temp 73
    temp at evaporator {little temp lead inside) about 53

    of course temp outside is 95-100

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: low duct temperature

    I would suspect that you have a refrigerant shortage.

    The only way to tell is to recover and check the amount against the nameplate charge.