    TXV icing but room warming



    Hello cool people,
    First time post for me.

    If your Thermal Expansion Valve and distributor lines are icing but your walk-in is warming above setpoint, what are the first things that should come to mind in terms of diagnostics?

    I just figure it is low on refrigerant but could somethin be wrong with the design?

    We're talkin 2HP Copeland w/ r134a for a 4c room.
    TXV is Alco with MOP thermal bulb charge.

    Thanks folks, Joe.



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: TXV icing but room warming

    1) Low on gas. Check SH, SC and eventually fill it up.
    2) Liquid solenoid blocked. Change diaphragm.
    3) Liquid filter clogged. Replace core.

  3. #3
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: TXV icing but room warming

    Quote Originally Posted by NoNickName
    1) Low on gas. Check SH, SC and eventually fill it up.
    2) Liquid solenoid blocked. Change diaphragm.
    3) Liquid filter clogged. Replace core.
    4) Lack of subcooling, poor refrigerant quality after the expansion valve

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  4. #4
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: TXV icing but room warming

    Strainer on inlet of TXV partially plugged

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: TXV icing but room warming

    If your Thermal Expansion Valve and distributor lines are icing but your walk-in is warming above setpoint, what are the first things that should come to mind in terms of diagnostics?
    Obviously the evaporator is not full of liquid and so the duty is reduced. Why it is not full of liquid is subject to investigation.

  6. #6
    Join Date
    Oct 2004
    Location
    USA
    Age
    65
    Posts
    24
    Rep Power
    0

    Re: TXV icing but room warming

    Thanks all.
    And Frank, can I be in your foursome?
    Joe

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: TXV icing but room warming

    Quote Originally Posted by liptow
    Thanks all.
    And Frank, can I be in your foursome?
    Joe
    have you got any clubs?

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: TXV icing but room warming

    What's a 4c room? I personally like more a 5 W room
    Pressures readings?
    Temeprature readings SH and SC?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    Jun 2006
    Location
    Victoria
    Age
    44
    Posts
    27
    Rep Power
    0

    Re: TXV icing but room warming

    I play golf, do I qualify?

Similar Threads

  1. troubleshoot a two door storage room
    By duraid in forum Fundamentals
    Replies: 7
    Last Post: 13-12-2006, 06:57 AM
  2. Cheese Room Design 24V DC
    By jbelding in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2006, 03:23 PM
  3. Installation of cold room
    By Josip in forum Legal-Business-Marketing
    Replies: 12
    Last Post: 12-03-2006, 09:20 PM
  4. Freezer Room Panels
    By Feeze in forum Technical Discussions
    Replies: 10
    Last Post: 22-04-2005, 05:58 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •