    Hello cool people,
    First time post for me.
    If your Thermal Expansion Valve and distributor lines are icing but your walk-in is warming above setpoint, what are the first things that should come to mind in terms of diagnostics?
    I just figure it is low on refrigerant but could somethin be wrong with the design?
    We're talkin 2HP Copeland w/ r134a for a 4c room.
    TXV is Alco with MOP thermal bulb charge.
    Thanks folks, Joe.
    Mar 2006
    Merate (LC) - Italy
    2,549
    Re: TXV icing but room warming
    1) Low on gas. Check SH, SC and eventually fill it up.
    2) Liquid solenoid blocked. Change diaphragm.
    3) Liquid filter clogged. Replace core.
    Jun 2001
    N.Ireland
    1,630
    Quote Originally Posted by NoNickName
    4) Lack of subcooling, poor refrigerant quality after the expansion valve
    Kind Regards Andy
    Jun 2005
    California
    394
    Strainer on inlet of TXV partially plugged
    Oct 2001
    Nottingham UK
    5,667
    Obviously the evaporator is not full of liquid and so the duty is reduced. Why it is not full of liquid is subject to investigation.
    Oct 2004
    65
    Thanks all.
    And Frank, can I be in your foursome?
    Joe
    Oct 2001
    Nottingham UK
    5,667
    Quote Originally Posted by liptow
    Thanks all.
    Joe
    have you got any clubs?
    Oct 2003
    5,630
    34
    What's a 4c room? I personally like more a 5 W room
    Pressures readings?
    Temeprature readings SH and SC?
    Jun 2006
    Victoria
    44
    27
    I play golf, do I qualify?
  1. troubleshoot a two door storage room
    By duraid in forum Fundamentals
    Last Post: 13-12-2006, 06:57 AM
  2. Cheese Room Design 24V DC
    By jbelding in forum Fundamentals
    Last Post: 02-04-2006, 03:23 PM
  3. Installation of cold room
    By Josip in forum Legal-Business-Marketing
    Last Post: 12-03-2006, 09:20 PM
  4. Freezer Room Panels
    By Feeze in forum Technical Discussions
    Last Post: 22-04-2005, 05:58 AM