    How much *****
    What is the typical ***** charge for a 5-ton split system? i.e. How many pounds (or Kg) would it take to refill the system after a leak? The unit in question is a Goodman.
    Apr 2006
    1,620
    Re: How much *****
    TXV or Cap Tube?
    FYI there is no real set weight, you have to do it according to Super heat or sub cooling and tune it to the units unique characteristics
    Apr 2006
    Libya
    Re: How much *****
    As the previous member said you have to charge with regards to superheat and the outdoor ambient temp.,but
    I will give you an estimate weight if it uses R407c then
    it will be about 5 kg and .
    Feb 2006
    derbyshire
    610
    Re: How much *****
    use the sight glass !!
    Sep 2003
    ISRAEL
    72
    4,248
    Re: How much *****
    Hi Mike,
    Why not call a pro?
    It sounds as you are not one, while he tops it up, ask for an explanation.
    Chemi
    Feb 2001
    phoenix,arizona
    72
    103
    Re: How much *****
    Look at the side panel, there is a lable, it will tell you how much ***** required for a standard installation. But...If your line set is longer, or you added filter drier, you would need to add a little more to compensate for it...normally not much.
    Best to call the pro. call the factory or local distributor for a list of qualify contractor.
    Be Happy
    May 2006
    philippines
    5
    Re: How much *****
    you may use a manifold guage and then youll know how much freomn you are charging to your unit
    Mar 2006
    Philippines
    124
    Re: How much *****
    Quote Originally Posted by yhruhteb
    That is pressure not the quantity of refrigerant.
    Guapo
    Apr 2006
    1,620
    Re: How much *****
    and both are totally useless, you must tune it to the system, the cookie cutter method is shoty at best and a sign of truly bad workmanship, the only way to do it right is to tune it to the needs of the system, there IS NO SET AMOUNT !!
    May 2006
    58
    14
    Re: How much *****
    The unit charge will vary based on length of line set. You have to charge the unit based on superheat or subcooling (depending on your metering device.) Sight glasses are useful sometimes, but shouldn't be relied upon to tell you if the system is low on gas; one of our servicemen pulled 30# of R-22 from a system which had been overcharged by a maintenance engineer who was clearing the glass-the condenser was plugged solid, and he didn't have a guage on the high side to see what was going on. Make sure your coils are clean, filters are clean, belts tightened properly, etc. before you think about adding gas to a system.
    Nov 2008
    Foshan,Guangdong,China
    22
    Re: How much *****
    R404a or R407C.
    11,025
    Re: How much *****
    Quote Originally Posted by ice_cool View Post
    R404a or R407C.
    What ?! Your answer is meaningless.
  1. Water in *****
    By chemi-cool in forum Refrigerants
    Last Post: 17-08-2009, 10:16 PM
  2. ***** 404 A
    By Levin in forum Technical Discussions
    Last Post: 18-08-2003, 08:45 PM
  3. ***** System Pressure Relief
    By trong40 in forum Fundamentals
    Last Post: 31-07-2003, 12:26 PM
  4. Adding *****
    By M Kalisher in forum Domestic
    Last Post: 12-05-2003, 05:20 PM
  5. Noobie question.Evaporator Pressure.
    By kfjoe in forum Fundamentals
    Last Post: 04-03-2003, 09:11 PM