    dakin controller



    looking for some help with the field settings on a dakin controller (brc1d528) have changed the field setting for the remote thermostat sensor to off (not use) , but i'm contolling 2 splits off one controller . Does this adjustment mean that the splits will work off there air on temp individually. any help would be greatful.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: dakin controller

    Quote Originally Posted by mike live
    looking for some help with the field settings on a dakin controller (brc1d528) have changed the field setting for the remote thermostat sensor to off (not use) , but i'm contolling 2 splits off one controller . Does this adjustment mean that the splits will work off there air on temp individually. any help would be greatful.
    Are the splits in the same room?

  3. #3
    Join Date
    Jun 2006
    Location
    england
    Posts
    25
    Rep Power
    0

    Re: dakin controller

    yes there in the same room.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: dakin controller

    2 x split systems on one controller will each signal the outdoor units individually on achieving set point.

    Sorry about the previous question, I first thought you were controlling a twin split off one controller - it's been a long day 14 hours today and a total loss on a fridge load last night

  5. #5
    Join Date
    Jun 2006
    Location
    england
    Posts
    25
    Rep Power
    0

    Re: dakin controller

    cheers frank for the replies.
    would there be a way of forcing an inverter system to run at 100% so to check the running amps and gas pressures or have i completely got the wrong idea on inverter systems

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: dakin controller

    Put the unit into test mode which will force the system to override the stat setting.

    With the inverter systems, it may take some 10/15 minutes for the comp to ramp up to full speed - have patience and keep an eye on the gauges. The pressures seem to hang steady for ages then slowly increase.

Similar Threads

  1. Micro-cool controller
    By bernard in forum Supermarket Refrigeration
    Replies: 6
    Last Post: 25-08-2006, 07:10 AM
  2. Help with new electronic refrigerator controller !
    By EngiGal in forum New Technologies
    Replies: 17
    Last Post: 08-04-2006, 07:39 PM
  3. Controller wiring
    By Mickvee in forum Air Conditioning
    Replies: 2
    Last Post: 30-12-2005, 02:04 AM
  4. Replies: 4
    Last Post: 27-10-2003, 10:43 AM
  5. Fan Controller
    By Abe in forum Trouble Shooting
    Replies: 4
    Last Post: 12-01-2002, 02:21 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •