Results 1 to 50 of 131
Thread: Superheat
Hybrid View
-
19-05-2007, 11:53 AM #1
Re: Superheat
if you turn the screw on the expansion device half a turn how many degress would you expect it to rise or fall? Whats the general rule of thumb per turn?
-
20-05-2007, 06:05 AM #2
Re: Superheat
Hi there,
As far as I have read, there is no rule of thumb for this. Every manufacturer gives the info.
Also this changes with the model of TEV. For example for TE2 (Danfoss) half a turn gives some superheat change and for TE5, TE12.. (Danfoss), half a turn gives another change in superheat.
CheersEven Einstein Asked Questions
-
20-05-2007, 09:44 AM #3
Re: Superheat
Ok cheers lana
-
21-01-2008, 06:51 PM #4
Re: Superheat
The general rule is: TXV's almost never go out of adjustment. Assuming it was adjusted properly to begin with:
If the superheat is high then:
a. The evap air in temp is high or...
b. The refrigerant charge is low or...
c. The inlet screen is plugged or...
d. The TXV is undersized or...
e. Somebody has been screwing around with the adjustment.
If the superheat is low then:
a. The airflow through the coil is insufficient or...
b. The system is grossly overcharged or...
c. The compressor is inefficient (broken valves) or...
d. The TXV is oversized or...
e. Somebody has been screwing around with the adjustment.
Sadly, the most common reason I have found for adjusting TXV's is "e".
Similar Threads
-
TXV Superheat
By Gary in forum Trouble ShootingReplies: 15Last Post: 24-04-2011, 02:51 PM -
Carrier 23xl chiller-Low discharge superheat alarms
By Bradysmill in forum Trouble ShootingReplies: 7Last Post: 25-04-2010, 07:43 PM -
TEV superheat setting and low temperatures
By DaBit in forum FundamentalsReplies: 11Last Post: 01-03-2010, 02:11 AM -
Superheat debate
By zolar1 in forum Technical DiscussionsReplies: 5Last Post: 08-02-2008, 09:57 PM -
Superheat