Results 1 to 50 of 131
Thread: Superheat
Threaded View
-
27-07-2009, 06:50 AM #19
Re: Superheat
As Gary says, you can't have negative superheat, more like subcooling which suggests that you have liquid floodback to your compressor.
The difference between genius and stupidity is that genius has its limits.
Marc
Similar Threads
-
TXV Superheat
By Gary in forum Trouble ShootingReplies: 15Last Post: 24-04-2011, 02:51 PM -
Carrier 23xl chiller-Low discharge superheat alarms
By Bradysmill in forum Trouble ShootingReplies: 7Last Post: 25-04-2010, 07:43 PM -
TEV superheat setting and low temperatures
By DaBit in forum FundamentalsReplies: 11Last Post: 01-03-2010, 02:11 AM -
Superheat debate
By zolar1 in forum Technical DiscussionsReplies: 5Last Post: 08-02-2008, 09:57 PM -
Superheat
By shogun7 in forum FundamentalsReplies: 24Last Post: 23-08-2004, 05:54 PM