    Suggestions please? Worrying compressor noise from Fujitsu ASY 30E



    HI,

    I am looking for some suggestions on why a 4 year old single phase Fujitsu ASY 30E 8kw R407C non inverter unit makes a worrying comp noise on start up.

    As the condenser cycles / starts, it sounds like the compressor is starting properly but then followed by a deep vibrating noise and what sounds like the compressor going through a surge, this lasts for 2 seconds and then operation resumes normally, the hi pressure is fine, the low is 5psi down. Suctions line starts to freeze after some time, although minor and i am told this is not uncommon for these units. Could this be flooding / and the comp stalling, any other suggestions / tests. I am sure the charge is near correct as it was weighed in last year, it may be 30g over at the most.

    Many thanks
    Last edited by MrThin; 26-06-2006 at 10:32 PM.



  2. #2
    Join Date
    May 2006
    Location
    china
    Posts
    98
    Rep Power
    18

    Re: Any Ideas? Worrying noise from Fujitsu ASY 30E

    Hi, MrThin(are u really a slim guy?), I regard the big noise may be due to liquid refrigerant migration, does the compressor have a crankheater?the evap. pressure is too low, the temperature of R407C in 5 psi is -31 F, it's not the range of air conditioning.. if your refrigerant charge is correct, there may be blockage in suction lines..

  3. #3
    Join Date
    Jun 2006
    Location
    England
    Age
    47
    Posts
    4
    Rep Power
    0

    Re: Any Ideas? Worrying noise from Fujitsu ASY 30E

    Hi, thanks for the suggestion, i will check with Fujitsu technical but i dont think it can be the crank heater as it happens when the unit has been running for some time in high ambient. The low press is around 100 psi, i remember checking it against spec for conditions and it being 5 below spec. Think i will have to into more detail and recover, re charge and watch pressures whilst noise occurs. Just thought it might have been a known prioblem with unit.

  4. #4
    Join Date
    Jul 2001
    Location
    Good bay
    Posts
    50
    Rep Power
    24

    Re: Any Ideas? Worrying noise from Fujitsu ASY 30E

    The low press is around 100 psi, i remember checking it against spec for conditions and it being 5 below spec.
    Low Pressure of 100 psi is too high. If it used for Airconditioning Low Pressure should be around 65-75psig.
    Setrite

    A group of Donkey's Led by a Lion can defeat a group of Lion's led by a Donkey

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Any Ideas? Worrying noise from Fujitsu ASY 30E

    Quote Originally Posted by setrite
    Low Pressure of 100 psi is too high. If it used for Airconditioning Low Pressure should be around 65-75psig.
    a difficult statement to make when you don't know at what frequency the compressor is running and if the system has non-condensibles

  6. #6
    rbartlett's Avatar
    rbartlett Guest

    Re: Any Ideas? Worrying noise from Fujitsu ASY 30E

    Quote Originally Posted by frank
    a difficult statement to make when you don't know at what frequency the compressor is running and if the system has non-condensibles
    A non inverter Frank non inverter...;-))

    However if you check the chart the suction should -as mentioned- be nearer 65psig. You appear to have overcharged it

    Cheers

    Richard

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Any Ideas? Worrying noise from Fujitsu ASY 30E

    Quote Originally Posted by rbartlett
    A non inverter Frank non inverter...;-))

    Cheers

    Richard
    OOOOOPPPPS

  8. #8
    Join Date
    Jun 2006
    Location
    England
    Age
    47
    Posts
    4
    Rep Power
    0

    Re: Any Ideas? Worrying noise from Fujitsu ASY 30E

    Sorry for the inaccurate info, trying to remember the readings and made a mistake. It must have been around the 60 psi mark, got confused thinking R410a,I will get the gauges on it and come back with accurate readings, temps etc. My intial querie was is their a common cause for this type of compressor surging? I am thinking of measuring current to comp during and after this condition to see what i can find.

  9. #9
    Join Date
    Nov 2004
    Location
    Nottingham
    Posts
    37
    Rep Power
    0

    Re: Any Ideas? Worrying noise from Fujitsu ASY 30E

    is the comp recip. or scroll? older toshiba recip's made this awfull noise too, check amps & voltage for sure. Power supply adequate? is system in domestic/smaller commercial application where mains power isn't really up to running Aoy 30 fixed speed system, this unit does start about 65 amp

  10. #10
    Join Date
    Nov 2004
    Location
    Nottingham
    Posts
    37
    Rep Power
    0

    Re: Any Ideas? Worrying noise from Fujitsu ASY 30E

    suction pressure on 407c 48-62psig, you will find frosting common too

Similar Threads

  1. your opinons on fujitsu please
    By acgibo in forum Air Conditioning
    Replies: 18
    Last Post: 26-08-2009, 05:06 PM
  2. desperately seeking fujitsu
    By rbartlett in forum Air Conditioning
    Replies: 7
    Last Post: 04-08-2007, 09:06 PM
  3. noise inverter compressor
    By Airclima in forum Air Conditioning
    Replies: 1
    Last Post: 26-07-2007, 11:42 PM
  4. fujitsu tech info
    By Krups in forum Air Conditioning
    Replies: 11
    Last Post: 01-12-2005, 07:41 PM
  5. Noise Levels
    By Daddy Cool in forum Tools and Calculators
    Replies: 15
    Last Post: 07-04-2005, 02:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •