Results 1 to 6 of 6
09-02-2022, 03:34 PM #1
Vilter VSS1851 capacity calculation
Hello,
Is there somebody abble to select a Vilter single screw compressor (software required).
I'm in need of capacity and schaft power consumption at the following conditions:
- Compressor type Vilter VSS 1851
- Refrigerant ammonia
- Revolution 3000 rpm
- Saturated suction temperature -44,07°C => -47,3°F
- Suction non usefull superheat 4°K => 7,2°F
- Saturated discharge temperature +27,7°C =>81,9°F
- Liquid subcooling 2°K =>3,6°F
- Non economized
many thanks
09-02-2022, 09:12 PM #2
Re: Vilter VSS1851 capacity calculation
Hi, cricri,
found this maybe can be of some help to you ...
https://climate.emerson.com/en-sg/to...ction-software
Best regards, Josip
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
09-02-2022, 09:31 PM #3
Thanks Josip, but no calculation possibility with this link.
They don't want to share their Soft, Probably the end of my professional Email address frighten them...
09-02-2022, 10:23 PM #4
Hi, cricri
cannot promise anything,
but I can ask one of my friend for help.
Not sure, but I believe they have Vilter software.
I can ask him tomorrow.
Best regards, Josip
10-02-2022, 06:17 AM #5
Thank you Josip,
I forgot to mention that oil cooling is liquid; (éthylène glycol)
11-02-2022, 12:43 PM #6
Hi, cricri ...
check your email ...