    EBM axial fan with VFD drives



    Hi everyone. Does anyone have experience driving EBM axial fans with Variable Frecuency drives ? More specifically, we are trying to set up condensing temperature control for a chiller which has 2 A6D910 fans with a Schneider ATV310HU15N4 VFD.

    The thing is, EBM says they do not recommend using fans with VFDs beause there is a potential bearing premature damage and we have reasons to believe this maybe true (but thousands of different applications with VFDs claiming they are perfectly ok to be used).

    Regards



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: EBM axial fan with VFD drives


  3. #3
    Join Date
    Jan 2022
    Location
    Canada
    Posts
    1
    Rep Power
    0

    Re: EBM axial fan with VFD drives

    I have seen EPM motor or equivalent run with VFD a couple of time.
    Many manufacturer are using those motors on there setup.

    If you are afraid for the bearing there is filtering solution at the VFD outlet to control the voltage spike.

    DV-Dt filters are one solution

    Sine wave filter are a more efficient solution

  4. #4
    Join Date
    Aug 2005
    Location
    ARGENTINA
    Age
    59
    Posts
    26
    Rep Power
    0

    Re: EBM axial fan with VFD drives

    Quote Originally Posted by frank View Post

    Yes. The guy seems to know what he´s talking about. Describes the kind of issues we are worried about. Thanks