    location of capillary tube



    hi all
    i notice that all split a/c systems :
    the location of capillary tube is within the condensing out side unit not within evaporator inside unit.
    my question : why?



  2. #2
    rbartlett's Avatar
    rbartlett Guest

    Re: location of capillary tube

    Quote Originally Posted by afeef
    hi all
    i notice that all split a/c systems :
    the location of capillary tube is within the condensing out side unit not within evaporator inside unit.
    my question : why?

    my answer

    why not?

    cheers

    richard

  3. #3
    Join Date
    May 2006
    Location
    Leicestershire
    Age
    58
    Posts
    28
    Rep Power
    0

    Re: location of capillary tube

    With this system there is no liquid line thus reducing refrigerant charges,this means higher efficiency and smaller compressors with no liquid being pumped around a system.
    Yuo do need to remember that critical charges are very important on these systems.

    regards

    andy

  4. #4
    rbartlett's Avatar
    rbartlett Guest

    Re: location of capillary tube

    Quote Originally Posted by andy bailess
    With this system there is no liquid line thus reducing refrigerant charges,this means higher efficiency and smaller compressors with no liquid being pumped around a system.
    Yuo do need to remember that critical charges are very important on these systems.

    regards

    andy
    I'm interested in a few things here..

    1) why does no liquid line mean higher efficiency
    2)why are smaller compressors needed in these systems
    3) why are these 'charge critical' when a Daikin is charged to 30 metres

    cheers

    richard

  5. #5
    Join Date
    Aug 2005
    Location
    iraq
    Age
    67
    Posts
    130
    Rep Power
    19

    Re: location of capillary tube

    my openion is :

    if we use the pipe running close to suction pipe as liquid line , this will give subcooling to liquid ,which will increase the efficincy of system.
    but using this pipe as part of evaporator will have heat loss along its length , this will degrease the efficincy.
    am i right??
    thanks

  6. #6
    Join Date
    Jun 2006
    Location
    Leicester
    Age
    34
    Posts
    18
    Rep Power
    0

    Re: location of capillary tube

    rbartlett my answer

    why not?

    cheers

    richard

    Not very helpful there Richard.Do you know why?

  7. #7
    rbartlett's Avatar
    rbartlett Guest

    Re: location of capillary tube

    Quote Originally Posted by wizzer
    rbartlett my answer

    why not?

    cheers

    richard

    Not very helpful there Richard.Do you know why?

    The answer was not quite a flippant as it seems. I was around when the first Japanese splits were imported in a major way so as I had just joined the design team of a well know UK manufacturer Qualitair who used a liquid line we had to ask this very question..Our head of design had just come back from japan on a fact finding mission and was quite shocked how far behind we were even though we though we were second biggest in the UK.
    I also knew Qualitair had no future when it started badge engineering Toshiba splits back in '83.

    This has been discussed here many times before but I'm now extremely interested in Andy's assertions so I won't join the debate till he answers my questions

    Cheers

    Richard

  8. #8
    Join Date
    Jun 2006
    Location
    Leicester
    Age
    34
    Posts
    18
    Rep Power
    0

    Smile Re: location of capillary tube

    This has been discussed here many times before but I'm now extremely interested in Andy's assertions so I won't join the debate till he answers my questions

    Cheers

    Richard
    Thats a bit hard on Andy's reply i have heard many engineers say the same thing,and i have read far worse posts in this forum than that from non engineers.

    I would love to know your answers on the above and why andy's assertions are wrong please enlighten us all who have been told the same thing.

    P.S i'll pick up your answer tomorrow early start
    Last edited by Brian_UK; 26-06-2006 at 10:38 PM. Reason: Added 1st [quote] command

  9. #9
    Join Date
    Jun 2006
    Location
    los CaBOS MEXICO
    Age
    63
    Posts
    5
    Rep Power
    0

    Re: location of capillary tube

    Hi Guys.......
    You Will Find Answers Checking Out R-22 P-h Charts

  10. #10
    rbartlett's Avatar
    rbartlett Guest

    Re: location of capillary tube

    Quote Originally Posted by wizzer
    Thats a bit hard on Andy's reply i have heard many engineers say the same thing,and i have read far worse posts in this forum than that from non engineers.

    I would love to know your answers on the above and why andy's assertions are wrong please enlighten us all who have been told the same thing.

    P.S i'll pick up your answer tomorrow early start

    At no point have I said Andy was wrong.


    Cheers

    Richard

  11. #11
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: location of capillary tube

    The reason why they do it is simple: to avoid the 'sssssssissing sound' you should hear when they install it in the indoor unit.
    Second reason, easier to fabricate a heatpump when all the controls are in the outdoor unit.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  12. #12
    Join Date
    Aug 2005
    Location
    iraq
    Age
    67
    Posts
    130
    Rep Power
    19

    Re: location of capillary tube

    oh ,,,yes peter , i beleve you are right
    the sssssing sound is one of the reasons to locate the capillary at the out side unit
    good point ,,,,,thanks
    afeef

  13. #13
    Join Date
    Apr 2006
    Location
    Libya
    Posts
    18
    Rep Power
    0

    Re: location of capillary tube

    I want to say not all split systems have outdoor capillary
    tubes ,some of them are indoor capillaries ,and as they mentioned above it is a matter of cost .

  14. #14
    Join Date
    Jun 2006
    Location
    India
    Age
    63
    Posts
    28
    Rep Power
    0

    Re: location of capillary tube

    EARLIER

    Locating the capillary close to the cooling coil is certainly, benificial with a view to better COP/ EER of the system.

    But it is experienced that doing so, it usually produces unpleasent intermittent Hissing sound due to flow of refrigerant. Also it may creat "Kir-Kir" sound as the coiled capillary vibrate in it self as the varying quantity of the refrigerant metered to evaporator due to varying load.

    To avoid this sound the usual practice was to wrape the coiled capillary with wet & oiled glass putty. but it does not provide complete and permanent solution.

    NOW

    Later on during 80's some AC manufacturers started putting capillary at the condensing unit and tried to keep the sound out with the condensing unit which is remotely placed.

    Yes, this resulted the soundless cooling unit compromising with the poor COP comparatively.

    What else, yes, this is the total thermal comfort of human being.
    Last edited by S.K.VARDE; 08-07-2006 at 02:53 PM.

  15. #15
    Join Date
    Jun 2006
    Location
    Leicester
    Age
    34
    Posts
    18
    Rep Power
    0

    Re: location of capillary tube

    Who's bothered as long as it works

  16. #16
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: location of capillary tube

    I'm botherd if my machinery is wasting more power then needed!

Similar Threads

  1. capillary tube design
    By Chris Zahrt in forum Fundamentals
    Replies: 5
    Last Post: 04-06-2009, 09:16 PM
  2. Capillary tube prices in the UK
    By trial in forum Fundamentals
    Replies: 4
    Last Post: 18-09-2007, 12:16 PM
  3. :rolleyes: capillary tube size in distributor?
    By abbasi in forum New Technologies
    Replies: 2
    Last Post: 08-07-2006, 03:56 PM
  4. metric capillary tube
    By tralex in forum Fundamentals
    Replies: 5
    Last Post: 21-02-2006, 06:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •