    Daikin VRV-IV HR - "H3-05" error



    Hi everyone.

    Did anybody get the "H3-05" in REYQ-T?
    REYQ-T - H3-05.jpg
    Classic "H3" - "Malfunction of HP-switch". But for REYQ it is "Connection malfunction main PCB <> inv.2 PCB"

    In my case seems to be the "LC-14" - "Transmission error between main PCB (A1P) - inv.2 PCB (A6P)"
    REYQ-T - LC-14.jpg

    Inv.2 PCB A6P was replaced about 1 month ago.
    Last edited by R666A; 15-12-2021 at 01:22 PM.



  2. #2
    Join Date
    Oct 2013
    Location
    Ukraine
    Posts
    14
    Rep Power
    0

    Re: Daikin VRV-IV HR - "H3-05" error

    Ahahah. When I assemblied power modules conn. X6A was inserted so weakly. During defrost compressor has high rpm and vibration ))))))