    Cvhg



    Good day Engineers,

    Could someone please help.

    What could be the reasons for a Trane CVHG, adaptiview tracer CH530 to display ALARM: Compressor did not accelerate shutdown?

    Thank you



  2. #2
    Join Date
    Apr 2011
    Location
    Russia
    Age
    51
    Posts
    139
    Rep Power
    16

    Re: Cvhg

    Probably current have not been detected by current transformers. Or controller did not get feedback from aux contacts of main contactor.

  3. #3
    Join Date
    Jun 2016
    Location
    Nigeria
    Posts
    64
    Rep Power
    8

    Re: Cvhg

    Thank you Mr Alex for your suggestion, it is my first time of working on CVHG unit and I did not perform any thorough check on the unit..
    The next time I go to that site, I will check just as you have suggested.
    Thanks