    Feb 2011
    scotland
    454
    screw compressor oil safety switches
    On screw compressors with none pumped oil feeds relying on discharge pressure only, other than oil flow switches, what other safety devices have you come across? Mainly thinking about when theres no or little oil in the seperater.
    3,356
    Re: screw compressor oil safety switches
    Seanf,
    Oil level switch, no oil level then no oil.
    oil flow switch,
    discharge to suction differential,
    discharge to oil header differential,
    cold start valve to build up differential quickly,
    discharge temperature as no oil for cooling cuts out pretty quickly.
    low oil filter differential pressure
    high oil filter differential
    A lot of combinations can be used, but oil level pretty important.
    Feb 2011
    scotland
    454
    Cheers Ranger.
    Should have said, mainly thinking in terms of when theres no or little oil in the seperater.
    Feb 2011
    scotland
    454
    Seanf,
    oil flow switch,
    discharge to suction differential, Just for sufficent pressure when you have oil, or do you start getting discharge gas blowing back to suction giving a low diff when theres no oil to block clearances?
    discharge temperature as no oil for cooling cuts out pretty quickly, Would you be expecting to see some damage caused though if it was to get to the point where discharge temp goes high from lack of oil?
    low oil filter differential pressure, Would that be for a blown out filter element, or for discharge gas passing through the filter element to easily?
    Cheers Ranger.
    Sean