    Question EVAPORATOR CHARGE ---> Questions



    Hello,

    I know these are basic questions that a HVAC Technician probably shouldn't ask,
    but, I'm getting a little confused.

    1. Why does a FROZEN EVAPORATOR indicate a LOW CHARGE? Shouldn't the refrigerent top-off at some saturated pressure and then build up sufficient SUPERHEAT to keep the coils from freezing?
    2. What are the symptoms of a FLOODED EVAPORATOR? Will that also freeze? Will the SUCTION LINE at the COMPRESSOR freeze-up?

    Thanks!



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: EVAPORATOR CHARGE ---> Questions

    1, A low charge allows the operating temperature to go below the norm for the system, hence frost and ice build up. As the ice builds up the transfer area decreases and the suction pressure gets lower and the ice builds up and so on.

    It doesn't some much 'top-out' more 'bottom out'

    2. The flooded evaporator may not freeze but you would suffer from frost etc on the suction at the compressor because the refrigerant is boiling it's way back to the compressor.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jun 2005
    Location
    California
    Posts
    395
    Rep Power
    19

    Re: EVAPORATOR CHARGE ---> Questions

    Quote Originally Posted by KETTLER
    Hello,

    I know these are basic questions that a HVAC Technician probably shouldn't ask,
    but, I'm getting a little confused.

    1. Why does a FROZEN EVAPORATOR indicate a LOW CHARGE? Shouldn't the refrigerent top-off at some saturated pressure and then build up sufficient SUPERHEAT to keep the coils from freezing?
    2. What are the symptoms of a FLOODED EVAPORATOR? Will that also freeze? Will the SUCTION LINE at the COMPRESSOR freeze-up?

    Thanks!
    A frozen evaporator can be the result of low/poor air flow, dirty filter/evaporator,low charge,defrost problems,
    defective control,etc,etc.
    A flooded evap will cause low superheat, delute the oil, break valves, and possibly destroy (scramble) the compressor. It will not freeze!

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: EVAPORATOR CHARGE ---> Questions

    Quote Originally Posted by KETTLER View Post
    Hello,

    I know these are basic questions that a HVAC Technician probably shouldn't ask,
    but, I'm getting a little confused.
    These are questions which reveal a basic misunderstanding of how a refrigeration system works and thus bring into question whether one is in fact a HVAC Techician. If you are a novice, just say so and we will try our best to advise you.

  5. #5
    Join Date
    Dec 2005
    Location
    Johor
    Age
    62
    Posts
    151
    Rep Power
    19

    Re: EVAPORATOR CHARGE ---> Questions

    Cheerio Gary

    Well said.
    Ugh..... In the first place was he refering to
    the plate freezers or walk in freezers .
    Lets design a freezer that should not be open at all and seal air tight forever n does not serve its purpose.
    Maybe no frost will develop on the tubing, no need defrosting mechanism and save everybody the trouble of maintenance

    HEHEHEHEHE.......

  6. #6
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    397
    Rep Power
    18

    Re: EVAPORATOR CHARGE ---> Questions

    A sealed freezer ????

    A scenario more for a quantum fridge engineer
    perhaps schroedinger( ) could shed some light especially if you sealed his cat in there.

Similar Threads

  1. Interview questions
    By zimbo in forum Chit Chat & Service Stories
    Replies: 16
    Last Post: 10-09-2008, 10:06 PM
  2. few questions
    By abbasi in forum Fundamentals
    Replies: 5
    Last Post: 16-07-2006, 11:28 AM
  3. some questions of air source hp
    By Lc_shi in forum Technical Discussions
    Replies: 3
    Last Post: 11-05-2006, 08:58 PM
  4. questions
    By parry in forum Chit Chat & Service Stories
    Replies: 17
    Last Post: 31-10-2005, 09:46 AM
  5. Starting a compressor, and receiver questions.
    By DaBit in forum Technical Speculations
    Replies: 9
    Last Post: 24-08-2002, 12:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •