    Question Hello and help please with daikin inverter



    Hi Iam having trouble with a Daikin inverter indoor model ftkd60jvea Outdoor model rkd60jvea. Indoor seems to run ok. The outdoor starts it runs for about 15 seconds then shuts down for 5 minutes then repeats. There is no fault showing on the remote. I dont have any sevice info on this model. thanks



  2. #2
    Join Date
    Nov 2005
    Location
    Southampton
    Age
    45
    Posts
    54
    Rep Power
    19

    Re: Hello and help please with daikin inverter

    in the uk you get the fault code (on IR controllers)
    by holding down the timer cancel button, there is a beep and "00" appears on screen. keep pressing cancel button and you'l hear a series of beeps (some single some double) when you hear a long beep that is the fault code.

    If the unit does actually start then there probably isn't a fault stopping unit. is the air short cycling?? is the evap frosting (daikin have frost prevention cutoff if coil too low)? is coil sensor (on evap) ok ?
    regards aeb200

  3. #3
    Join Date
    Jun 2006
    Location
    ATHENS / GLYFADA
    Age
    50
    Posts
    16
    Rep Power
    0

    Smile Re: Hello and help please with daikin inverter

    Quote Originally Posted by classic
    Hi Iam having trouble with a Daikin inverter indoor model ftkd60jvea Outdoor model rkd60jvea. Indoor seems to run ok. The outdoor starts it runs for about 15 seconds then shuts down for 5 minutes then repeats. There is no fault showing on the remote. I dont have any sevice info on this model. thanks
    Hello my friend .
    Tell me if it is a wall mounted or somethink other.
    I have all inverter models service manual of wall mounted type to email you if you send me your email.

  4. #4
    classic's Avatar
    classic Guest

    Re: Hello and help please with daikin inverter

    Hi. The unit is a wall hung multi split and my email is becks@ledanet.com.au thanks.

  5. #5
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Hello and help please with daikin inverter

    Probably too late for me to reply but...

    Take the cover off the outdoor and check the LED's when it is trying to start.

    Sounds like the outdoor control board is faulty.

    Either that or the compressor is faulty.If that is the case the board will probably be faulty anyway.

    Was the fault code L5?

  6. #6
    Join Date
    May 2006
    Location
    Norwich
    Age
    53
    Posts
    134
    Rep Power
    18

    Re: Hello and help please with daikin inverter

    The green flashing LEds on the outside unit will help to find the fault

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Hello and help please with daikin inverter

    Quote Originally Posted by S_Line
    The green flashing LEds on the outside unit will help to find the fault
    Green flashing LED's - I thought they were RED

  8. #8
    yasif's Avatar
    yasif Guest

    Re: Hello and help please with daikin inverter

    I agree with aeb200. In these similar situations where indoor coil frosts, You would get the error code "C4" on the remote control.

  9. #9
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    425
    Rep Power
    20

    Re: Hello and help please with daikin inverter

    I know that the guy originally posted this in 2006,and has probably fixed it by now, but the last time I had that fault on a daikin, it was the compressor. Something to do with the rotor position sensor - the forth wire on the comp. New compressor sorted it.