Results 1 to 2 of 2
Thread: Electronic expansion valves
29-09-2021, 03:06 AM #1
29-09-2021, 12:17 PM #2
Re: Electronic expansion valves
Electronic can flood back if set wrong or fail so the main advantage is better control and
they respond faster.
With a traditional thermostatic valve the open / close cycle is over about 6 DegsC (or 6K)
so there is always a delay or a lag in response to the valve opening and closing. The 6K diff
gives added protection against flood back.
With an electronic valve that differential can be reduced to less than 1 DegC (1K) so they
are far more responsive.
Rob