    Re: Fan speed issue on Mitsubishi

    If the installer is due back to have another look, ask him to take the following readings both before it ramps up and then after the fan speed increase so that these can be compared against the data in the service manual:

    Indoor coil temperature
    Indoor air temperature
    Indoor humidity
    Outdoor temperature
    Compressor frequency
    Suction gas pressure

    What position have you set for the swing flap?
    Does the same problem occur when you select 'Econo' mode?
    How long is the pipeline between indoor/outdoor units?

    Sound pressure level
    Indoor
    Cooling (Hi/Me/Lo) 44/ 39 / 24
    Heating (Hi/Me/Lo) 48 / 41 / 30
    Outdoor Cooling/Heating 51/ 51

    The fan sound levels do not look high (compared to some)