Thread: Fan speed issue on Mitsubishi
Hybrid View
-
02-09-2021, 10:44 AM #1
Re: Fan speed issue on Mitsubishi
If the installer is due back to have another look, ask him to take the following readings both before it ramps up and then after the fan speed increase so that these can be compared against the data in the service manual:
Indoor coil temperature
Indoor air temperature
Indoor humidity
Outdoor temperature
Compressor frequency
Suction gas pressure
What position have you set for the swing flap?
Does the same problem occur when you select 'Econo' mode?
How long is the pipeline between indoor/outdoor units?
Sound pressure level
IndoorCooling (Hi/Me/Lo) 44/ 39 / 24 Heating (Hi/Me/Lo) 48 / 41 / 30 Outdoor Cooling/Heating 51/ 51
The fan sound levels do not look high (compared to some)Last edited by frank; 02-09-2021 at 10:51 AM.