    Exclamation !!big Daikin Problem!! Codes,u4,pj, And E0



    Hi Guys
    Got a daikin A/C split with a indoor wall mounted unit (R410A). installed by another company.Never worked i got called in showing a fault U4. past experiance of a U4 code on the daikin means outdoor PCB. Checked outoor unit and LED A was not lighting which also indicates outoor pcb. Bought a new pcb and came with a capacitor which had to be added to the pcb. Changed the pcb but the fuse blew straight away. Discoverd mix up in wiring and sorted out wiring. then coming up code PJ as soon as i switched it on.I fitted the capacitor wire which came with the unit and now it is coming up with the code E0 as soon as i switch it on rang up daikin tech and they said to check all the safety devices to see if they all are sending 240v to the devices and 240v coming back. all fine except only 24v being sent and coming back to the low pressure device.the pcb is fine what do i do now??? PLEASE HELP



  2. #2
    Join Date
    Mar 2006
    Location
    Glasgow, Scotland
    Posts
    177
    Rep Power
    19

    Re: !!big Daikin Problem!! Codes,u4,pj, And E0

    Your first fault code U4 Basically means the indoor unit is not communicating with the outdoor!. PJ means you have changed the PCB and not installed the capacity adapter with the new board. E0 means that one of the outdoor safetys have tripped. To help you anymore we would need the model numbers of the system.

  3. #3
    Join Date
    Jun 2006
    Location
    midlands
    Age
    43
    Posts
    11
    Rep Power
    0

    Re: !!big Daikin Problem!! Codes,u4,pj, And E0

    i know the indoor model No is
    FAQ71BUV1B

    i will have to find the outdoor i have it written somewhere

  4. #4
    Join Date
    Jun 2006
    Location
    midlands
    Age
    43
    Posts
    11
    Rep Power
    0

    Re: !!big Daikin Problem!! Codes,u4,pj, And E0

    the outdoor model No is
    RR71B7V3B

    thanks for the quick response

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: !!big Daikin Problem!! Codes,u4,pj, And E0

    Quote Originally Posted by airconengineer
    the outdoor model No is
    RR71B7V3B

    thanks for the quick response
    Single phase non-inverter compressor.
    U4 code on the daikin means outdoor PCB.
    Incorrect. U4 means that the indoor unit cannot communicate with the outdoor unit.
    Changed the pcb but the fuse blew straight away.
    Doh!
    the pcb is fine what do i do now


    Are you now saying that the outdoor pcb LED is flashing (green one) and the U4 fault has gone? is the only fault code now EO?

    Have you carefully checked the connectors on the new pcb (the grey ones)? Does the system run first then fault with EO or refuse to run?

    If it refuses to run from cold and just shows an EO then I would suspect that you have got a wiring problem. Pull off the grey wire connectors and check for continuity (through the fan and compressor). If you have continuity here then it may be that the connectors are not seated correctly or are on the wrong pins

  6. #6
    Join Date
    Jun 2006
    Location
    midlands
    Age
    43
    Posts
    11
    Rep Power
    0

    Re: !!big Daikin Problem!! Codes,u4,pj, And E0

    yes the u4 fault has gone away now the problem is the EO code. and it refuses to run even in fan only mode the wiring is correct and im sure the pcb connectors are fine.

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: !!big Daikin Problem!! Codes,u4,pj, And E0

    and im sure the pcb connectors are fine.
    Sometimes you can't see the wood for the trees

  8. #8
    Join Date
    Jun 2006
    Location
    midlands
    Age
    43
    Posts
    11
    Rep Power
    0

    Re: !!big Daikin Problem!! Codes,u4,pj, And E0

    okay im certian.my main concern is only 24v being sent and coming back from the low pressure switch but the rest having 240v

  9. #9
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: !!big Daikin Problem!! Codes,u4,pj, And E0

    The LP switch has nothing to do with an EO fault. An interuption to the 240 volt being sent out on one grey wire and back on the other will give an EO stoppage. Resetting the main power will, under normal circumstances, reset the EO fault and allow the system to run until it faults again. If you can't clear the fault then either, 1) you have a permanant open circuit through either the compressor or 2) through the fan motor, or 3) a wiring problem on the grey wires.
    EO means - outdoor protection device activated.

  10. #10
    Join Date
    Jun 2006
    Location
    midlands
    Age
    43
    Posts
    11
    Rep Power
    0

    Re: !!big Daikin Problem!! Codes,u4,pj, And E0

    thanks for responding.whats the best way of going about checking if theres an open ciruit on either of the three and once found how can it be fixed??

  11. #11
    rbartlett's Avatar
    rbartlett Guest

    Re: !!big Daikin Problem!! Codes,u4,pj, And E0

    Quote Originally Posted by airconengineer
    thanks for responding.whats the best way of going about checking if theres an open ciruit on either of the three and once found how can it be fixed??
    please don't, that poor Daikin has suffered enough -this is bordering upon cruelty ..

    Call a real live 'airconengineer' who will sort it PDQ

    Cheers

    Richard

  12. #12
    Join Date
    Feb 2005
    Location
    Jamaica
    Posts
    121
    Rep Power
    20

    Re: !!big Daikin Problem!! Codes,u4,pj, And E0

    come on RB give the chap a chance life is also a learning process,we all were not born big,help him grow.

  13. #13
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24

    Re: !!big Daikin Problem!! Codes,u4,pj, And E0

    Quote Originally Posted by airconengineer
    thanks for responding.whats the best way of going about checking if theres an open ciruit on either of the three and once found how can it be fixed??
    A mulitimeter, but then you would know that if you worked on air con.

    Best talk to your local college and apply for a training course

    Then equip yourself with the proper Diakin manuals (you can download them off the Diakin web site (link on the right hand side)

    Get stuck in and learn there is no short cut to effort

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  14. #14
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: !!big Daikin Problem!! Codes,u4,pj, And E0

    Quote Originally Posted by airconengineer
    thanks for responding.whats the best way of going about checking if theres an open ciruit on either of the three and once found how can it be fixed??
    Frank wrote
    Pull off the grey wire connectors and check for continuity (through the fan and compressor). If you have continuity here then it may be that the connectors are not seated correctly or are on the wrong pins

  15. #15
    Join Date
    Jun 2006
    Location
    midlands
    Age
    43
    Posts
    11
    Rep Power
    0

    Smile Re: !!big Daikin Problem!! Codes,u4,pj, And E0

    thanks for the lecture lads. i know how to use a multimeter so rest assured. i was thinkin more in the lines of being able to override the device to test which one of the three is broken

  16. #16
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: !!big Daikin Problem!! Codes,u4,pj, And E0

    Quote Originally Posted by airconengineer
    thanks for the lecture lads. i know how to use a multimeter so rest assured. i was thinkin more in the lines of being able to override the device to test which one of the three is broken
    Frank wrote
    An interuption to the 240 volt being sent out on one grey wire and back on the other will give an EO stoppage.
    All the clues are there - you're just not reading them

  17. #17
    Join Date
    Jun 2006
    Location
    midlands
    Age
    43
    Posts
    11
    Rep Power
    0

    Thumbs up Re: !!big Daikin Problem!! Codes,u4,pj, And E0

    ive written previously about that

    "my main concern is only 24v being sent and coming back from the low pressure switch but the rest having 240v"

  18. #18
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: !!big Daikin Problem!! Codes,u4,pj, And E0

    my main concern is only 24v being sent and coming back from the low pressure switch
    The LP switch has nothing to do with an EO fault.
    More indication of a wiring problem

    GREY WIRES = EO Fault

  19. #19
    Join Date
    Jun 2006
    Location
    midlands
    Age
    43
    Posts
    11
    Rep Power
    0

    Re: !!big Daikin Problem!! Codes,u4,pj, And E0

    I have checked the wiring twice. i rekon the people who installed it wired it wrong, started it up,made a bang, corrected the wires and when it didnt work they ran home to watch the world cup.

    you think this is a possibilty

  20. #20
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: !!big Daikin Problem!! Codes,u4,pj, And E0

    I have checked the wiring twice
    What about continuity? Did you check this?

  21. #21
    Join Date
    Apr 2007
    Location
    england
    Age
    42
    Posts
    29
    Rep Power
    0

    Re: !!big Daikin Problem!! Codes,u4,pj, And E0

    sounds like compressor, capacitors or fan motor to me

  22. #22
    Join Date
    Nov 2006
    Location
    Cheshire, UK
    Age
    56
    Posts
    360
    Rep Power
    18

    Re: !!big Daikin Problem!! Codes,u4,pj, And E0

    Quote Originally Posted by cooldude View Post
    sounds like compressor, capacitors or fan motor to me


    Nothing like casting your Net wide is there?

Similar Threads

  1. Problem with ducted Daikin
    By jutty in forum Trouble Shooting
    Replies: 8
    Last Post: 23-07-2007, 05:34 AM
  2. Strange problem
    By Peter_1 in forum Electrical
    Replies: 9
    Last Post: 10-04-2007, 05:19 PM
  3. Daikin FH series problem
    By pdingle in forum Air Conditioning
    Replies: 7
    Last Post: 13-08-2006, 06:45 PM
  4. Daikin problem
    By Jambo in forum Trouble Shooting
    Replies: 4
    Last Post: 28-07-2006, 07:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •