greetings friends
I'm not familiar with trane RTHD unit configuration C1D6E5 and saw one chiller running but showing “capacity limited by liquid level “ chiller is first time started and noticed ExpV fully open and approach for cond and evap are 0.5c (EChWT13.4/LChWT13.1 DP7psi)(ECoWT25.8/LCoWT26.3/DP 10psi)and the suc pressure is high 455kp sat T 12.8/ discharge 697kpa sat T 26.5 .. dis Supperheat 10c / amps around 110. Is this because of soft loading or low liquid level. Any tips?