    Hi all

    Just fitted a split unit as above,looking at the refrigerant charge chart.It gives the quantity for pipe length one way only.Are they already taking into account its x2,or do i have to x2.
    Here's the link to the chart :-

    https://www.manualslib.com/manual/11...page=20#manual

    A previous Mitsubishi unit i fitted it just gave a simple per metre measurement.

    Thanks all
    Matt



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Mitsubishi MUZ-GE25va(charge question)

    Unit is charged for 7m.
    Additional charge is 30g/m for any length over 7m. So for a 10m indoor/outdoor pipe length you would add 3 x 30g.
    Additional charge is only measured on the liquid line.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Mitsubishi MUZ-GE25va(charge question)

    This unit is also giving a simple per metre measurement.

    Although this unit uses the entire pipework and indoor unit as the evaporator the suction pipe should be almost 100% vapour.

    The discharge line to the indoor unit is is after the unit expansion device so could be considered to be in a mixed state. Therefore you only need to add refrigerant to maintain the required state in the discharge line.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Apr 2021
    Location
    uk
    Posts
    5
    Rep Power
    0

    Re: Mitsubishi MUZ-GE25va(charge question)

    Thanks for the clarification chaps.
    :-)

  5. #5
    Join Date
    Apr 2021
    Location
    uk
    Posts
    5
    Rep Power
    0

    Re: Mitsubishi MUZ-GE25va(charge question)

    Hi again
    I'm fitting a toshiba unit now in the lounge ,its an rav-sm800,does the same apply,
    this is the charge table http://www.toshiba-aircon.co.uk/asse...sion_11_5c.pdf

    .so would be 40g/m one way,{i don't include the return,as it were}
    in the installation it says total pipe length
    https://www.manualslib.com/manual/92...?page=3#manual

  6. #6
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Mitsubishi MUZ-GE25va(charge question)

    It'll be the same as before, one way only.
    Health and safety first..........unless I'm in a hurry.