23-06-2006, 03:25 AM #1
capillary tubes
I never work on capillary tubes systems. I just want to clarify what the symptoms of an overcharge are, and symptoms of an undercharge?
-
23-06-2006, 11:27 PM #2
Re: capillary tubes
As a system goes undercharged you will begin to see frost/ice build up on the coil then that will fall back to the capillary itself.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
24-06-2006, 07:49 AM #3
Re: capillary tubes
Capillary units are a critically charge system. You have to be pretty exact with the refrigerant charge. A correctly charge capillary unit will have no frosting on the capillary where it enters the evaporator, warm dryer, and your head pressure will be at spec. Under charged symptoms are low back pressure, frosting on capillary, cool dryer, low discharge temperature/pressure, low efficiency in cooling. A over charged system will have a high discharge temperature/pressure, hot dryer, higher suction pressure, usually on capillary system they have a suction line accumulator for when the unit is on off cycle the high-low sides equalize through the capillary to stop flooding to compressor when starting up, if you have frosting on accumulator whilst running can also indicate that unit is slightly over-charged.
Hope this helped
Similar Threads
-
Selection of capillary tubes
By patrickj in forum CommercialReplies: 11Last Post: 19-06-2008, 02:45 PM -
metric capillary tube
By tralex in forum FundamentalsReplies: 5Last Post: 21-02-2006, 06:57 AM -
Obstructed Capillary Tubes
By terrygoodrich in forum Trouble ShootingReplies: 9Last Post: 17-03-2005, 02:48 PM -
capillary tubes and mass flow when fed with liquid/gas
By DaBit in forum FundamentalsReplies: 15Last Post: 24-10-2002, 06:52 PM -
Capillary Tubes
By subzero*psia in forum DomesticReplies: 19Last Post: 26-06-2001, 11:56 PM