    Lowering maximum temperature



    I got a freezer that can go to maximum -15 degrees now.

    Would it be able to go to -20 degrees if I change the thermostat max settings?



  2. #2
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Lowering maximum temperature

    Hi
    Main thing is that .
    But to give you right answer need to know more about your system
    Type of refrigerant and compressor.

  3. #3
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Lowering maximum temperature

    .

    Minus 15 for a freezer is unusual.
    Minus 20 is more like the normal.

    Are you sure this is a freezer?

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Lowering maximum temperature

    Did it go to lower temperatures before now?

    What is ambient temperature around the freezer?

    Has anything changed since first installation?

    Is compressor running still at -15 or is thermostat still calling for compressor?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Jul 2021
    Location
    Singapore
    Posts
    2
    Rep Power
    0

    Re: Lowering maximum temperature

    No, it did not go below -15.

    Compressor model: L76CZ1
    Refrigerant: R134A

    Understand that R134A is not able to go to lower temperature. Must be R404A, correct?

  6. #6
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Lowering maximum temperature

    .

    If it is this comp then Minus 23 evap temp equates to about minus 13 case temp.

    https://www.womacool.com/productinfo/284992.html


    So if it is at minus 15 then you are at the limits of the comp.

    Rob


    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  7. #7
    Join Date
    Aug 2021
    Location
    Scotland
    Posts
    14
    Rep Power
    0

    Re: Lowering maximum temperature

    On 134a comp would need to run in vac on suction to achieve -20, which is never a good idea unless it is a special design, for low temp should be 448A, 449A, 407A or F, but on a 134a system may well require different pipework sizing, would probably be better to replace with a properly specified system.