    Air distribution



    I have a 4000 sq ft retail space, and there are 2 roof top units of 5 Tons each one, this place is going to be an office place, the offices have different dimensions.

    My question is How do I calculate the CFM's for each office?

    Thanks.

    Hernan



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Air distribution

    Quote Originally Posted by Herschmidt
    I have a 4000 sq ft retail space, and there are 2 roof top units of 5 Tons each one, this place is going to be an office place, the offices have different dimensions.

    My question is How do I calculate the CFM's for each office?

    Thanks.

    Hernan
    Hi Herman
    CFM will be a product of the duty required to cool the roon sensible and latent and the number of air changes/hour you require. You could have a variable air valume system where CFM varies with load
    If you can't fix it leave it that no one else will:rolleyes:

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Air distribution

    Quote Originally Posted by Herschmidt
    I have a 4000 sq ft retail space, and there are 2 roof top units of 5 Tons each one, this place is going to be an office place, the offices have different dimensions.

    My question is How do I calculate the CFM's for each office?

    Thanks.

    Hernan
    If you already have the roof top units installed then your only option is to balance the system down proportionally. Work out each room volume and then calculate the room volume as a percentage of the total volume. Now balance the air flow accordingly.

    Don't forget though that each room must also have a return air path back to the roof top for proper operation.

  4. #4
    Join Date
    Jun 2006
    Location
    India
    Age
    63
    Posts
    28
    Rep Power
    0

    Re: Air distribution

    You will have to calculate the heat load (in TR) of individual office blocks. Then propornate the CFM as for 1TR to 400 CFM. Don't forget to get back the return air to the unit in the same proportion. You may require redesigning of the air destribution system and balancing the same.

Similar Threads

  1. air cooler uneven distribution check
    By Lc_shi in forum Fundamentals
    Replies: 5
    Last Post: 17-06-2006, 12:47 AM
  2. air distribution in island
    By tralex in forum Supermarket Refrigeration
    Replies: 8
    Last Post: 06-04-2006, 02:33 AM
  3. Liquid Refrigerant Pumping
    By bersaga in forum Technical Discussions
    Replies: 34
    Last Post: 09-08-2003, 08:07 PM
  4. R507 in an R134a compressor: system design
    By DaBit in forum Technical Speculations
    Replies: 17
    Last Post: 01-05-2003, 09:25 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •