    R507 efficiency decrease verses R12



    We have some large refrigeration units running on R12 that need to get changed out . Can anyone tell me how much capacity are we going to lose by switching from R12 to R507 ?



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: R507 efficiency decrease verses R12

    Chris,

    Can you provide an example of one system and the operating temperatures? That might help to make any explanation more meaningful.

    PS. Welcome to the RE site.

  3. #3
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: R507 efficiency decrease verses R12

    Chris, you should gain capacity, not lose it. But if you are changing units out, why do you worry about losing capacity, since you should be able to match the new units' capacity to the load. I don't understand your question.

  4. #4
    Chris Moser's Avatar
    Chris Moser Guest

    Re: R507 efficiency decrease verses R12

    We have a process heat duty of 455 tons of refrigeration being handled by 4 refrigeration units arranged in parallel . We want to convert the units from running with R12 to R507. While I know nothing about the details of what is required to change out the fluid I expected that trying to run at the same operating conditions as we now do with R12 would result in a reduction in refrigerating capacity using the same equipment . So my first thought is how much reduction will I see , and how many of the 4 units will I need to change out completely to recover capacity ?

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: R507 efficiency decrease verses R12

    Chris,

    What are the operating conditions of the system? Evaporating and condensing temperatures please.

    Are you using screw compressors with economizers?

    Are you talking about completely changing the systems, or converting them to R-507 from R-12?

  6. #6
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: R507 efficiency decrease verses R12

    Quote Originally Posted by Chris Moser
    We have a process heat duty of 455 tons of refrigeration being handled by 4 refrigeration units arranged in parallel . We want to convert the units from running with R12 to R507. While I know nothing about the details of what is required to change out the fluid I expected that trying to run at the same operating conditions as we now do with R12 would result in a reduction in refrigerating capacity using the same equipment . So my first thought is how much reduction will I see , and how many of the 4 units will I need to change out completely to recover capacity ?
    Chris wrong gas to convert to
    try R134a, matches the pressures in the old system better. R507 will not work, equipment for R12 is not rated for the higher pressures (the compressors might) but the condensers and evaporators, pipes and valves will all be incorrect.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  7. #7
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: R507 efficiency decrease verses R12

    Chris, a 4RA-1000 compressor using R12 is capable of 67890 btu/hr at 20 deg F. This same compressor with a larger motor provides about double this capacity at the same conditions with R507. A 4RA-2000 is capable of 122,946 Btu/hr. Same displacement, but twice as much capacity and horsepower. I don't know why you think R507 has less capacity than R12.

    If you choose to use the same compressors, you will have to upgrade the motors. You will be abandoning compressors, not adding compressors. You will have to pipe the remaining compressors to the now abandoned condensers. Andy's advice is a much more sensible and less troublesome solution. Use 134A.

  8. #8
    Join Date
    Jun 2006
    Location
    USA
    Age
    58
    Posts
    42
    Rep Power
    0

    Re: R507 efficiency decrease verses R12

    R507 is a permanent replacement for R502 and like Andy said its the wrong application for a R12 retrofit,Why don’t you try using 414B? I have used it extensively with great results, it mixes will with mineral oil and the operating pressure are R12 like.

Similar Threads

  1. R507 in an R134a compressor: any danger?
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 21-12-2009, 12:44 AM
  2. Replies: 5
    Last Post: 24-07-2006, 03:28 PM
  3. R507 in an R134a compressor: system design
    By DaBit in forum Technical Speculations
    Replies: 17
    Last Post: 01-05-2003, 09:25 AM
  4. Replies: 2
    Last Post: 18-09-2001, 05:15 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •