    Cool PHE - condenser Water - NH3, add plates but now can't close



    HI,
    We open a PHE condenser water - NH3, we were getting high pressure and a huge differential pressure on the water side on PHE.
    So we decided to open and add 10 more plates.
    Model M10 - BWREF Alfa Laval
    But now we are having problem's to close the PHE. We don't manage to close without leak.
    Because we added more plates, I have no idea which should be the distance between the fix and back frame, neither Nm for tighetening.
    Also if I invert each plate, so cold side and hot side alternate, the plate does NOT align.
    Somebody have any good idea here?
    Much appreciatte.
    I have the Alfa Laval manual instructions, but not much help there.
    Thanks

    Dani



  2. #2
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,036
    Blog Entries
    4
    Rep Power
    31

    Re: PHE - condenser Water - NH3, add plates but now can't close

    you should contact Alfa Laval...

    when they sell you plates they should also inform you of the new distance.

    There is no Torque/NM for tightening, there is a set distance that has to be between the fixed and moving main plates.

    when you added the 10 plates you should have had to give the serial number to Alfa Laval and they should have given you the new measurement.

    also make sure to tighten it evenly between the eight bolts, when you reach the minimum measurement it should be spot on for all the bolts
    -Cheers-

    Tycho

  3. #3
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: PHE - condenser Water - NH3, add plates but now can't close

    Hi
    On PHE when you opened it you should change the all rubber gaskets and close that very carefully and gently and tight it with torque
    Last edited by mbc; 10-06-2021 at 07:09 PM.

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,355
    Rep Power
    39

    Re: PHE - condenser Water - NH3, add plates but now can't close

    Quote Originally Posted by PEPELEBU View Post
    HI,
    We open a PHE condenser water - NH3, we were getting high pressure and a huge differential pressure on the water side on PHE.
    So we decided to open and add 10 more plates.
    Model M10 - BWREF Alfa Laval
    But now we are having problem's to close the PHE. We don't manage to close without leak.
    Because we added more plates, I have no idea which should be the distance between the fix and back frame, neither Nm for tighetening.
    Also if I invert each plate, so cold side and hot side alternate, the plate does NOT align.
    Somebody have any good idea here?
    Much appreciatte.
    I have the Alfa Laval manual instructions, but not much help there.
    Thanks

    Dani
    As Tycho & MBC have said, but also you have to clean existing plates, not just add to them, unless new.
    Inverting plates, is that what instructions say?
    Usually "0" ring for ammonia inlet/outlet has to be replaces as a minimum.
    PHE, if bigger units they use 4 hydraulic power packs that you can hire to drive up simultaneously.

  5. #5
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,036
    Blog Entries
    4
    Rep Power
    31

    Re: PHE - condenser Water - NH3, add plates but now can't close

    this is before and after removing all the plates, pressurewashing them.
    needed three guys in a bucket line to pass the plates in, over and around all the pipes

    first time we did this one 10 years ago I was with a guy from Alfa and he brought the powerpacks RANGER1 mentioned, sadly there was no room

    -Cheers-

    Tycho

  6. #6
    Join Date
    Apr 2009
    Location
    Durban
    Age
    41
    Posts
    31
    Rep Power
    0

    Re: PHE - condenser Water - NH3, add plates but now can't close

    In addition to the good points above. There is a certain tightening sequence that must be adhered to. Confirming that all port and cassette gaskets must be replaced for all plates. PHE's can be a bugger - enjoy.