expansion valve
Hi guys,
We have air handling unit (A/C system) and a thermostatic expansion valve.
We have to fasten thermostatic bulb of expansion valve on suction pipe or should put bulb in drift of DX coil air outlet ?
Which one is correct ?
Thanks.
-
05-06-2021, 05:54 PM #2
Re: expansion valve
The bulb should be fastened to the suction pipe in accordance with the manufacturers instructions.
You will find some useful information from Sporlan here, highly recommended...
http://solutions.parker.com/SporlanliteratureBrian - Newton Abbot, Devon, UK
Retired March 2015
-
16-06-2021, 10:40 AM #3
Re: expansion valve
It should be fixed on the suction line and has to be insulated so as to operate on right super heat