    Cross-section pipe issue.



    Hi there.

    I have a question. I will try to describe it shortly.

    My refrigeration system has a water-cooled shell tube R22 condenser. The R22 inlet pipe has Ø 50mm (2 inches). The outlet pipe has Ø 40mm (1½ inches). I’ve installed the shutoff valve in the outlet pipe Ø 25mm (1inch). I used conical pipe reducers from both sides of the shutoff valve to install it. The valve is fully opened and R22 goes to the R22 receiver from the R22 condenser.

    My question is: Could I have made some changes in my refrigeration system, especially relatively to condensing pressure and temperature by reducing the pipe cross-section with the shutoff valve?

    Thanks in advance.

    Andrei.



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Cross-section pipe issue.

    Andrey,
    Any particular reason you put in smaller valve, was it all you had available?
    If to small you could bank up liquid in shell & tube condenser causing higher discharge pressures.
    Liquid receiver may not be able to breath or vent into condenser also not allowing to drain correctly.

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Cross-section pipe issue.

    Are you talking about the water pipework or refrigerant pipework?

    Seems strange that your inlet pipe size (50mm) is greater than the outlet pipe size (40mm)

  4. #4
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,036
    Blog Entries
    4
    Rep Power
    31

    Re: Cross-section pipe issue.

    I'm guessing there is a 1" equalizing line from the top of the receiver to the top of the condenser.
    so as long as the condenser is draining and you are not building up a level in the condenser itself I don't see any issue with it. (could be an issue when running high loads that the condenser doesn't drain fast enough)

    However, using a correct size valve would save you some welding
    -Cheers-

    Tycho

  5. #5
    Join Date
    Feb 2017
    Location
    Russia
    Age
    47
    Posts
    35
    Rep Power
    0

    Re: Cross-section pipe issue.

    Quote Originally Posted by RANGER1 View Post
    Andrey,
    Any particular reason you put in smaller valve, was it all you had available?
    If to small you could bank up liquid in shell & tube condenser causing higher discharge pressures.
    Liquid receiver may not be able to breath or vent into condenser also not allowing to drain correctly.
    Hi RANGER1.

    I installed the smaller valve because I didn't have any valves with a large diameter but I had to install it.

  6. #6
    Join Date
    Feb 2017
    Location
    Russia
    Age
    47
    Posts
    35
    Rep Power
    0

    Re: Cross-section pipe issue.

    Quote Originally Posted by frank View Post
    Are you talking about the water pipework or refrigerant pipework?

    Seems strange that your inlet pipe size (50mm) is greater than the outlet pipe size (40mm)
    Hello, frank.

    I'm talking about outlet refrigerant pipe. The inlet pipe has a greater diameter because we have two R22 condensers and they work simultaneously. R22 goes to both R22 condensers through one pipe.

  7. #7
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Cross-section pipe issue.

    Hi

    size of valves depending to our capacity ,
    so in small size the DP (droop pressure ) is high,
    also if you have not equalizing pipe you should go for larger size to let draining liquid from condenser and returning gas from receiver to condenser in this case of piping we should not have loop between condenser and receiver and slope of pipe should be high.

  8. #8
    Join Date
    Feb 2017
    Location
    Russia
    Age
    47
    Posts
    35
    Rep Power
    0

    Re: Cross-section pipe issue.

    Quote Originally Posted by mbc View Post
    Hi

    size of valves depending to our capacity ,
    so in small size the DP (droop pressure ) is high,
    also if you have not equalizing pipe you should go for larger size to let draining liquid from condenser and returning gas from receiver to condenser in this case of piping we should not have loop between condenser and receiver and slope of pipe should be high.
    Hi, mbc

    thanks for replying

    I have the equalizing pipe between receiver and condenser and the valve on this pipe is fully opened.
    Last edited by andrey7474; 12-05-2021 at 08:56 AM.

  9. #9
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Cross-section pipe issue.

    Actually you can check temperature of the liquid going to the receiver. If liquid sub cooled, it means that you have some liquid at the bottom of the condenser.