    VRV2 pipe blockage



    Good morning all,

    I've diagnosed a blockage in the refrigerant pipework on a Daikin RXQ8M8W1B system. Does anyone know if there is a built in filter/strainer, and where I can find it? Spoke to Daikin UK but they haven't got back to me yet.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: VRV2 pipe blockage

    VRV 2 are notorious for problems after a few years operating.

    Most circuit problems I used to encounter on these units were the EEV's failing

  3. #3
    Join Date
    Jun 2021
    Location
    Australia
    Posts
    6
    Rep Power
    0

    Re: VRV2 pipe blockage

    A lot of systems will run strainers before and after RMD, not usually accessible on AC systems though. You can usually find blockages easy by feeling the pipework until you feel a temperature drop over certain parts. Example is filter dryers, if they are blocked then they will be cold one side and warm the other due to the refrigerant not being able to pass through.