    Have a 4 hp Prestcold Unit, subsequent engineers working on this unit have "allowed" moisture and air ingress into system. Despite installing filters, one just before expansion valve, system goes into deep vacuum each time.

    Unit is a L400/0062 Prestcold running on Iceon R69
    Has a Oil Seperator, oil is a muddy brown colour. System has had leaks in the past, system operates on pump down, and pressure switch cuts at 14 inches vacuum !! Horror Horror

    Ive reset pressure switch to cut out at 5psig

    No wonder it has been sucking in air all this time.

    It has been suggested I replace all the oil, change oil seperator, change receiver tank, and replace Evaporator blower, and this shouls solve problem.
    Last edited by Abe; 07-07-2002 at 01:03 AM.



  2. #2
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27
    Marc,

    Thanks for your advice.

    Hope your dad enjoyed his trip up north, with gales and we have got snow this morning.

    Next time youre up, be sure to bring your dad up with you.

    I want him to enjoy a nice curry to warm him up and shake off the winter blues.

    Once again, thanks, speak soon

    Aiyub

  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    Why do you believe the problem is moisture? Is the oil separator working?

  4. #4
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Oil Separator

    When I apply warmth to the expansion valve I hear a "whoosh" and rushing sound as the built up gas surges as the ice plug I presume thats there melts.

    But the problem doesnt stop there. There is another area of built up pressure, I think at the filter drier, located just after the receiver.

    Filter is cold to the touch.

    After I opened up the TXV , this second "rush" of gas came sweeping by. Am I supposed to assume that the restriction was at the filter. Its a monstor big Sporlan valve, 1/2" pipe size.

    Or, is it something more sinister.................at the AC&R oil separator

    I dont know.........

    But Im ready to change oil..........

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    At low temps, oil can become very thick and act a lot like moisture. As the metering device warms, the oil thins out and passes through.

    This is common in cap tube cascade systems, but not impossible in TXV systems. It is much more likely if someone has added oil along the way. In addition, some refrigerants are not very good at carrying the oil.

    The tearing out of the hair is also a common symptom of oil problems.

    Is there a moisture indicator in the sightglass?
    Last edited by Gary; 31-12-2001 at 02:34 PM.

  6. #6
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27
    Gary

    The sight glass is very old with no moisture indicator and the glass looks a dirty brown shade.

    The temperature around these parts is around -6 C at the moment, the condensing unit is located near an open field, we had gale force winds gusting last week, and I worked Thursday night and all day Friday outside with the wind smacking into me.

    Hence, ( I want to tear my hair out)

    System has a back up unit, albeit smaller capacity, and this unit failed as well. Fortunately I sorted that one out, problem with the heat exchanger , blocked up, walls collapsed presumably.

    My engineer, is of course "on leave" I cant afford to pay him exhorbitant overtime this time of year, so yours truly was on call.

    And, this "service contract, I took it on just before Christmas, at the time I was rubbing my hands with glee, but now Im not too sure, Customers had his monies worth, I saved an awful lot of stock, hope he appreciates it.

    Hope this cold weather spell ends soon, I have to get back to sort the the whole thing out, enginneer is back tomorrow..........

    Im thinking..............I have just the job for him!!!!!
    I say with my "evil eye""" and a sly grin

    That will teach him !!!! He Heeeeeee

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    Happy New Year, Aiyub!!

    I always recommend moisture indicators, especially on low temp systems.

    The dirty brown shade in the glass might be another indication of dirty brown oil getting past the separator.

    Then there is the second surge through the drier. If it were ice plugged, why would it surge through without being warmed? If it is at a low point, it may provide a gathering point for oil after the TXV plugs. Then it could push the oil through when the TXV is unplugged.

    A temporary "fix" might be to change to ester oil, as it tends to flow much better at low temps, and the dirty stuff needs to be changed anyway. Don't be too surprised if the oil level rises as the excess is swept back to the compressor. You should change it several times.

    But the separator should be replaced ASAP.

    Passing the job to your engineer sounds like a great idea, but be sure to let us know how it works out.
    Last edited by Gary; 01-01-2002 at 04:47 PM.

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    Happy New Year, Marc!!

    These are all very good points, and I fully agree.

    To expand on this a bit, as I understand it, the high discharge temp (caused by high inlet superheat), cooks the oil giving it a muddy brown appearance, which then transfers to the glass.

  9. #9
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    To expand on this a bit, as I understand it, the high discharge temp (caused by high inlet superheat), cooks the oil giving it a muddy brown appearance, which then transfers to the glass.
    This is the usual case. When a dirty sightglass is observed on a refrigeration unit, the first order of business should be to replace the oil, and not simply rely on filter-drier changes to clean it up. And then consider replacing the sightglass. You should be able to save some of your hair this way...
    The POE reacts with the moisture to form a substance of bloody consistancy but waxy in appearance, this reaks havoc at the TEV and distributor.
    POE oil in the presence of moisture will hydrolyze to form a carboxylic acid, an organic acid which can damage the system. As a result, it is a good idea to use a filter-drier with some acid capacity when using POE oil.

    The waxy substances found in a refrigeration system using POE oil are more likely due to the fact that POE oil is an extremely effective solvent, far better than mineral or AB oil. Waxy substances present in the refrigeration tubing and compressor from manufacture will often not be bothered by mineral or AB oils, while POE oils will more likely to remove these substances. These waxes will flow in solution with the refrigerant and oil, and will precipitate out at the TEV port. Unfortunately, standard filter-driers are not effective in removing wax. Filter-driers which contain activated charcoal, however, (e.g., Sporlan "HH" filter-driers), are effective in removing wax.

    Wax can also be effectively removed by disassembling the TEV and cleaning it.... though it may do little to save what remaining hair you have on your head...
    Prof Sporlan

  10. #10
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27
    Marc,

    Thanks for the Trouble Shooting Data Collection sheet.
    I have printed it and will fill it out and complete it "NEXT WEEK"

    Why next week, you may ask?

    Well, I was ready, prepared to carry out the operation this weekend.

    But remember, I mentioned the freezer room has a standby system in place, which was repaired as well.

    Well, customer is quite happy that room is "working" and holding temperature, so he wants me to "delay" the job for a while.

    ie: he wants to delay parting with his cash by pushing the job away.......to another date

    Dont come this week he says, theres snow on the ground, and its cold, Come next week

    How thoughtful, how kind..........

    But wait, if that standby system breaks down tomorrow.......you can stand on your head and whistle thru your.............XXXX
    before you get me out there in the middle of the night!!!

  11. #11
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Organise

    Just so I organise myself for the job,

    How do I read/get measurements for the following:

    Saturated condensing temperature
    Do I read this off my pressure guage hooked up at the receiver end?

    Saturated evaporating tem
    Again, I presume I read this off my gauges pressure/temp chart


    COOLING MEDIUM SUPPLY TEMP

    I presume thats evaporator fans, supply temp is the temp of air entering the evaporator, or is it leaving the coil?


    I think I understand the rest
    Thanks in advance

  12. #12
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27
    I stripped the unit this weekend. I found an oily "sludge" contaminating the condenser right up to the filter. The oil seperator has obviously not being doing its job. System has had a ****tail of refrigerants added to compound the problem. I found bottles of 502. 69. 49, you name it , littered near the unit.

    I decided that changing oil to sort out "moisture" prob was not the answer. I wont get rid of the "oil lining" covering the liquid pipe right up from compressor to filter and beyond.

    I am going to replace all pipes and recondition compressor with new oil.

  13. #13
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27
    Hello Marc,

    Ive got the flu, banging headache, sneezes, runny nose, and just want to lie in bed all propped up with some fluffy pillows with the central heater on, and probably pretend to be very very ill so "nurse" the missus can run up the stairs and attend to my cries everynow and then and bring up steaming mugs of lemon and honey and lemsip!!

    And whilst in bed I can think of this blasted job at the ice cream factory, methinks the oil seperator didnt fullfill its job, ie: retain the oil and return it to the compressor sump.

    I found traces of this oily substance beyond the seperator, and I think this is what is blocking up the system, and moisture too.

    So to make things squeaky clean again, be a good idea to change the liquid line, new filter , new sight glass, also found the solonoid valve leaking, so that goes as well, refill compressor sump with new ester oil, charge with Isceon 69 and keep my fingers crossed.

    But will have to wait until I get/feel better. Winter is dragging on and Im dreaming of a holiday, somewhere warm, like Durban where all my relations have been holidaying over Xmas, Wild Coast more precise.

    But not sure about Durbs, its not I believe the same, so will have to think of someplace else. Got my house keys last week, so got the move to the new place to think about too, theres boxes everywhere, and packing, and wife browsing the MFI catalogue for a new kitchen

    Ok, Im losing it............I blame it on the Lemsip!!!

  14. #14
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27
    Sorry,

    If I had been paying attention...........like I should have done, all the ANSWERS are there already in your earlier postings

    I should have been more attentive.......so thanks once again for all the help I got on this one

    Dankie

  15. #15
    Jim Rushforth's Avatar
    Jim Rushforth Guest

    moisture

    Have you tried the triple evacuation method ? I have a leaflet on how it is done - would you like one ?

  16. #16
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27
    thanks

    Abe
    Last edited by Abe; 07-07-2002 at 01:04 AM.

  17. #17
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60
    Now, now Aiyub, control yourself

    Everyone should know how to do a triple evacuation and with a double salko I believe it's worth 7/10
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  18. #18
    Jim Rushforth's Avatar
    Jim Rushforth Guest
    Hi Again Abe,

    Couldn't get the file through as a .doc so am sending it to you
    as a j.peg

    Cheers - Jim

  19. #19
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27
    Jim

    Would you mind sending the *.doc file to my e mail address
    Look it up on my details

    Thanks

  20. #20
    Jim Rushforth's Avatar
    Jim Rushforth Guest
    Hi Abe

    Cannot contact you by e-mail - there is no access to your mail
    address.

    Did you receive the two-page file sent in jpeg format and the
    text notes ????

    Cheers - Jim

  21. #21
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    Is the problem resolved?


    I was wondering - DEEP VACUUM. What micron level have you brought it down to, and I assume you have no rise on a shut in? that would eliminate moisture if your down to 150-300 mic's and it it holds, indicating no ongoing evaporation of moisture as long as your not evacuating in an extremely cold ambient.

    The sysmptom regarding TEV observation sounds like moisture
    Last edited by herefishy; 24-01-2002 at 11:54 PM.

  22. #22
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    Triple Evacuation Procedure

    1. Evacuate the system (from both sides if possible) to 1000 microns.

    2. Break the vacuum (from the discharge access if possible) with dry nitrogen to slightly above atmospheric pressure.

    3. Evacuate the system (opening the low side access first) to 500 microns.

    4. Break the vacuum (from the discharge access if possible) with system refrigerant to slightly above atmospheric pressure.

    5. Evacuate the system (opening the low side access first) to 500 microns or less.

    6. Charge the system.

  23. #23
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    Some may find my procedure a little unorthodox. Here is the reasoning behind it:

    When a system is evacuated, approximately 10% of the old refrigerant is still in the system. Breaking the vacuum from the discharge port forces the old stuff through the system towards the suction line. If you then start the evacuation at the suction port, you will pull a higher percentage of old residual gas out.

    Breaking the vacuum with dry nitrogen is a BIG time saver, because the compressor oil will not absorb the nitrogen. The second evacuation will be very fast.

  24. #24
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Update on what happened here

    The system was very contaminated, the pressure switches were set to cut the unit on pump down in a vacuum setting, 15 inches

    The system had leaks, it had been sucking in air every time it went into pump down.

    Oil was sludged, the oil seperator didnt work. System was 15 years old.

    I took everything out and dumped the lot, including the evaporator

    Have fitted a new system in. Everything running well at -25 C

    Ok, I know, its like cheating, but as the medical profession puts it, delaying death wasnt the answer, the quality of life for that old system was not there, so I let it die, or more accurately I practiced Euthanasia on it!!!

    Thats all folks, and thanks a lot, I learnt a lot on that job with all the input I received.

  25. #25
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    I don't think that's cheating.... It's one thing to know how to fix it all and it's the same to recognize whether there is any value in doing it!

    I would say the (customer) could not realize any better value than the service that you rendered. Was it a hard sell?

  26. #26
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    I like the quote " delaying death wasn't the answer"

  27. #27
    Join Date
    Dec 2001
    Location
    U.S.A.
    Posts
    14
    Rep Power
    0

    Lightbulb the moisture problem

    Have you tried a 'dryer' on the system? In case you dont know what this is, it is a piece of tubing that attatches to the bottom of the evaporator right at the capillary tube. This piece is specifically designed for removing moisture from the sealed system when the system is opened (letting moisture in)...The trick to this piece of equipment, is that it has to be replaced EVERY time the sealed system is opened. So, if you install one now, then have sealed system work later, you need to install a new one at that time.

  28. #28
    brookbank's Avatar
    brookbank Guest
    ive found that when engineers say a system is full of moisture, it is usually the oil waxing in the system.
    Shell SD oil seems to be a lot better at low temperatures than Clavus 32 on R22 or when the discharge temperature is high
    change the oil.also check the suction superheat as this will raise discharge temperatures to a point that will kill oil

    the way i check a seperator is to disconnect the oil return and run it into a container, with the system running you should see a trickle of oil returning and no gas (honest)

    also if you let the seperator cool down and start the system back up, you can feel a temperature drop where the oil level is as the top of the seperator heats up and the oil stays cool

  29. #29
    4petes's Avatar
    4petes Guest
    I work for a very large commercial refrigeration contractor doing 90%supermarkets. just be done with it pull charge vacume unit change oil add gas and driers. had a store employee try to deice a low temp tub with a screwdriver hE punched A hole in coil sucked into vacume. major pain pulled 600 #refrigerant after trying to clean up system for over two weeks YOUR KILLING YOUR CUSTOMER WITH LABOR HE JUST WANTS IT TAKEN CARE OF. NEVER A COMPLAINT AFTER THIS WORK was done. what is head psi ? and does it equate to what the outlet of the condenser tube feels like. if it is cool but running high hp then you have non condensibles.

  30. #30
    Join Date
    Mar 2007
    Location
    bahran
    Posts
    1
    Rep Power
    0

    Thumbs up Re: Moisture

    Hi I am soma , i am a new member.

    i would like to say hello to all the member in this forums.

Similar Threads

  1. Maisotsenko cycle
    By Lc_shi in forum New Technologies
    Replies: 11
    Last Post: 17-07-2008, 01:35 PM
  2. Moisture in Propane Liquid
    By Nizar in forum Refrigerants
    Replies: 4
    Last Post: 24-07-2006, 04:12 PM
  3. Moisture loss calculation
    By gregorm in forum Technical Discussions
    Replies: 15
    Last Post: 15-05-2006, 04:23 PM
  4. Moisture bound insulation
    By Temprite in forum Commercial
    Replies: 2
    Last Post: 18-05-2005, 02:57 PM
  5. Article in ACH&R News
    By Gary in forum Fundamentals
    Replies: 8
    Last Post: 20-05-2003, 12:27 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •