    Dear friends,

    What helps cool rotary compressors ? As you know on scroll and hermetic and … compressors we cool compressor by return suction from evaporator. But at rotary compressor suction return gas enters directly to compressor by this reason accumulator is necessary for these types of compressors.
    Now, These type of compressors are not suction cool. How these types of compressors cool ?

    Thanks.



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Rotary compressor

    They dont. The body is at high pressure so it can get pretty hot.

  3. #3
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    138
    Rep Power
    21

    Re: Rotary compressor

    The vapour is discharged through the exhaust port into the compressor housing. Here the hot gas “cools down” the electric windings and oil. These components are designed to work happily in 100°C to 120°C.