Results 1 to 19 of 19
    Feb 2020
    Pakistan
    27
    Rating of Liquid Vapour Separator
    Can any one know how to check the rating of low side vapour liquid separator from a P&ID in a single stage system?
    For how many KW of refrigeration this vessel is going to work while planning for expansion of old system?
    Feb 2006
    poland
    49
    Re: Rating of Liquid Vapour Separator
    rize1159, redefine your question
    jest dobrze ale nie jest najgorzej
    3,361
    Quote Originally Posted by rize1159 View Post
    This could give you some idea, as I have no idea.
    https://www.haphillips.com/uploads/f..._WP-18E-01.pdf
    Jul 2006
    74
    865
    26
    This is a calculation I do not know precisely how to make. I always had a Design Engineer make the calculations.
    It is simple to use a catalog with smaller systems, but larger systems require a bit more knowledge.
    The factors involved (among others) are the density of the gas, how much liquid is in the return, and vessel design. Basically you are trying to slow down the velocity of the Refrigerant so that any liquid will fall out in the vessel before going to the compressor. The design of the vessel is also important. For instance you can increase the effective size of a vessel by introducing the flow from both ends.
    Wish I could be of more help.
    Nov 2009
    france
    64
    224
    Rize 1159,
    in summary
    you have to know on what side of the system is accepted the volume expansion (LP vessel or HP liquid receiver)
    if it's in LP vessel; 3 volumes are calculated:
    - minimum level to prime the pumps. min 200mm depend if there is a pot at the bottom and an ''anti-vortex''.
    - expansion volume above minimum volume. include coils volume, headers, condensers, all return liquid....
    this will set the high level switch position on the vessel at design + a safety margin.
    - separation volume above the max level
    - in this volume you have to calculate the gaz speed at design capacity (incude flash gaz from expansion device).
    This speed must comply with the maximum separation speed acceptable. Depend of shape (vertical/horizontal), number and position of return header and suction header, separation height, evaporation temperature.
    This is the old method of calculation, of course today there are sofwares .
    there are still tables and curves for the old calculation....
    beware, new LP vessel can be fitted with ''devices'' to improve liquid and gaz separation.=>smaler vessels.
    Brain storming:
    of course when all liquid is back in the expansion vessel (HP or LP). there is no possibillity to get the maximum capacity from evaporators....After long standstill you can.....
    Feb 2020
    Pakistan
    27
    Thanks Ranger1
    Feb 2020
    Pakistan
    27
    This is a LP side vessel.
    We can assume 50%level max. as a rule of thumb.
    It has only one suction line for vapours to compressors.
    It is horizontal vessel with one return line from evaporator and one liquid inlet from expansion valve.
    Problem: We have 03 parallel compressors operating from this vessel and quite OK. We want to add 02 more. This will increase vapour flow rate. But would we be having good separation effeciency?
    Diameter of vessel 1200mm and length is 3500mm. It is horizontal. Currently operating at 1800KW/-4C ammonia. Want to increase to 3000KW/-4C.
    Some are saying its OK and others are noding in negative. Quite confused
    3,361
    Rize1159,
    Can you advise pipe sizes on dry suction back to compressors
    Also high pressure liquid line.
    I am a guesser in this area, but this is what I come up with, also using Danfoss Coolselector for valves.
    Best get an engineer, as looks suspect.
    If you get any liquid carry over, high levels etc, very big chance of compressor damage & problems.
    As a minimum could also install suction slop pot, but if going to that trouble best off install new surge drum for new evaporators with new or upgraded suction & liquid lines.
    From H.A.PHILLIPS your vessel is to small
    1800kw = 512 tons 1371mm diameter x 3860 long suction line 250nb liquid line makeup 50nb
    3000kw= 853 tons 1828mm diameter x 4100mm long 300mm suction line liquid makeup line size 65nb
    Nov 2009
    france
    64
    224
    Rize1159,
    after calculation, 1800 kw ;-4°C / (supposed +35°C); level 600 mm in LP vessel D1200 x 3500 mm / NH3.
    calculated separation speed is 0,81 m/s.
    This value is matching exactly with the maximum speed allowed.
    you cannot imagine 3000 kW.
    Feb 2020
    Pakistan
    27
    Sorry guys, there is one mistake. I got confused with other vessel.
    Dia of vessel is 2000mm not 1200mm and length is 3000mm.
    Liquid make up after expansion valve is 65mm but compressor suction is 200mm.
    +35C condensing temperature is right assumption.
    I am little confused. with a minimum height of liquid 600mm, how 1.2m diameter of vessel will be justified for horizontal vessel. Shouldn't horizontal vessel be maximum half filled? In my calculation, it should be 3.7m dia for 1800KW.
    Feb 2020
    Pakistan
    27
    Rize1159,
    Can you explain it. I cant get you selection
    Nov 2009
    france
    64
    224
    Please check the position of your hight level safty switch, this is important for any further calculation.
    No, I cannot share a soft with you.
    diam 2000x lg 3000 is a strange size for a vessel....
    Apr 2009
    Durban
    41
    31
    Hi Bud,
    For 1800KW @ -4/+35 NH3 vessel sizes as follows:
    1.) Single separation horizontal vessel = your size must be minimum 2,55m long x 1,850mm wide. High level @ 925mm from bottom.
    2.) Double separation horizontal vessel = your size must be minimum 3,06mm long x 1,46mm wide. High level @ 730mm from bottom.
    I am conservative on allowable velocities but have not had any machines break.
    The above calculations assume that there is sufficient surge volume between minimum level and high level from defrosting of coils, etc.
    Calculations based on high level @ 1/2 way on vessel for quick check. More detail of plant and share P&ID can add more value to your query.
    Feb 2020
    Pakistan
    27
    [QUOTE=cricri;330435]
    it is mid way i.e 1000mm.
    I am asking name of software for purchasing option.
    Feb 2020
    Pakistan
    27
    I think you are using 0.5m/s velocity for height calculation. For length, can you explain a little more.
    I have question on it that how we are going to maintain separation height without consideration surge volume and max liquid level in vessel all the time. Should not calculation of dia of vessel be as below
    Separation height + max level allowed in vessel + surge volume height
    [/QUOTE]
    Attached P&ID
    Nov 2009
    france
    64
    224
    3000 kw ;-4°C / (supposed +35°C);1 return / 1 suction; level approx 1000 mm in LP vessel D2000 x 3000 mm / NH3.
    calculation tool Not availlable on the market
    Feb 2020
    Pakistan
    27
    Thanks cricri,
    As per calculation system seems ok for 3000KW?
    Nov 2009
    france
    64
    224
    Yes but it's with your inputs.
    I entered 4032lt return liquid to match with half level in the vessel.
    I entered also 1 return (worst situation), but from your PID it could be 2.
  19. #19
    Apr 2009
    Durban
    41
    31
    The minimum length is based on the velocity used x number of passes x staying time of 3 seconds. The rule that we use states if you double the stating time then you can multiply the velocity x 1.7 times. Velocity used @ 3 seconds @ -4 deg. C SST is 0,25m/s
    If this is a critical charge plant then you maintain separation height by the charge of the plant. Possibly the vessel is not sized for the full charge required?