    Is this correct?



    I recently came across these slides from an Embraco training video. I was sure that the metering device was always connected to the lowest point on the evaperator, but these slides say otherwise, or am I missing something?
    Attached Images Attached Images



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Is this correct?

    That's just what your pictures are showing, can you not see that?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Nov 2020
    Location
    Taiwan
    Posts
    25
    Rep Power
    0

    Re: Is this correct?

    So you agree with this?

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Is this correct?

    yes, it will allow any remaining refrigerant to drain out of the evaporator at the end of the cooling cycle.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Is this correct?

    In the picture where the inlet is at the bottom, Embraco do not recommend it.
    In the other picture where the inlet is at the top, Embraco recommend it.

    Bottom feeding is for flooded evaporator.