    Unhappy Compressor Cooling wrong unit



    Hi!

    I am a layman desperate for an answer. I turn on one aircon and it will not cool. I go to the other room and find the aircon that is turned off (not switched on for days) is so cold it has condensation.

    I had a professional look at it a week ago. He opened some valves and told us to leave them running until they came good. That seemed to work initially, but now I'm dealing with the problem above.

    I can't find any info beyond a blogger telling me to clean the filter. All new units, four in total. The other two units have not had any issues.

    Many thanks,

    Aryne



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Compressor Cooling wrong unit

    Unit interconnecting piping needs to be checked for correct pairing.

    Also electrical wiring including remote controls needs checking.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Compressor Cooling wrong unit

    There's more units fitted like that than you'd think, only noticeable when one of them is turned off.

    Like Brian says, Unit A inside is piped to A outside but the interconnecting cable goes to B outside. Outdoor unit sees B calling for coolling so that's why it will eventually freeze up.
    Get the installing company back to commission it a bit more thoroughly or if your are desperate and competent swap outdoor interconnect of those two units and try each indoor one at a time.
    Cheers,
    Andy.

  4. #4
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Compressor Cooling wrong unit

    the interconnecting cables are crossed system a is wired to system b and b to a

  5. #5
    Join Date
    Feb 2021
    Location
    Australia
    Posts
    3
    Rep Power
    0

    Re: Compressor Cooling wrong unit

    Thank you so much!! Really appreciate it!

  6. #6
    Join Date
    Feb 2021
    Location
    Australia
    Posts
    3
    Rep Power
    0

    Re: Compressor Cooling wrong unit

    Thanks very, very much guys! I will call them up and let them know. You're angels!!