    Make Daikin FDY140FV1 sense Temp from Wall Control



    Our Client in Australia has 3 x old Fan Coils installed
    FDY140FV1
    FDY125FV1B
    FDY71PV1A
    We confirm these units have P1 & P2 which Daikin Tech Help said means the coils are compatible with new/current controls.

    We need to be able to make these air conditioners sense directly from
    their current 3 x BRC1B52/62 wall controls,
    or
    an Upgraded wall control (eg. a Modern BRC1E63)
    Confirming
    • A (3x) new wall control for each will be acceptable
    (required as the current controllers turn out not to have sensors)
    • A remote stand-alone temp sensor will not satisfy the requirement.

    Using the original BRC1B52/62 Wall control We tried the below field codes to no avail.
    o 50-40.1 as instructed by Tech Help.
    o 10.2.01 as per the attached which is for BRC1C62 https://www.youtube.com/watch?v=5MxSSuZVz90

    Daikin Tech said
    • current control has no sensor behind the on the Air slots wall control
    o (Customer has confirmed this, photo attached …)
    So it makes sense why above would not work...

    Subsequently we connected a BRC1E63 to P1 & P2 on one of the units (each indoor has P1 & P2)

    We tried the below field codes to no avail:
    o 20-2-03 usual “Modern” code for Sensor @ Control
    o 50-40.1 as instructed by Tech Help.
    o 10-2.01 as per the attached which is for BRC1C62 https://www.youtube.com/watch?v=5MxSSuZVz90
    Those didn’t work either.

    If you made it this far let's talk about time management skills later :-)

    TLDR
    either we need a working field code for the old coil and the modern control or some kind of work around.

    I’ve tried googling only can’t find anything helpful; where to from here please?

    All help gratefully appreciated & thanks in advance.
    Last edited by sirplus; 13-02-2021 at 02:15 AM.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Make Daikin FDY140FV1 sense Temp from Wall Control

    10-2.01 as per the attached which is for BRC1C62

    It should be 10:2:03 for remote controller thermistor. Watch the Youtube video that you linked again.

  3. #3
    Join Date
    Mar 2021
    Location
    United States
    Posts
    2
    Rep Power
    0

    Re: Make Daikin FDY140FV1 sense Temp from Wall Control

    I have recently purchased this model from Home Appliances Coupons and I am also facing the same problem in starting, So one of my friends came and said to visit youtube and see its controlling tutorials so now I am easily operating this.