    E2-01 error Daikin Altherma 3



    Hello!! Please help if anyone know about Daikin Altherma 3. I have a consistent error E2-01 (earth leakage detected by pcb assy). The chiller works well for 2 or 3 hours before showing the E2-01 error. I have change everything, the hydrobox(indoor unit) pcb, all the outdoor unit changed and the same error. Outdoor unit is EPGA16DAV3 and the indoor unit is EABH16DA9W
    Regards
    Attached Images Attached Images



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: E2-01 error Daikin Altherma 3



    E2 Earth Leakage by Leak Detection PCB Assy

    Remote Controller Display
    Method of Error Detection
    Failure is to be detected by using leak detection PCB assy.
    Error Decision Conditions
    Leakage is detected under the conditions outside of the scope of high pressure switch operation.
    Supposed Causes - Defective compressor

  3. #3
    Join Date
    Mar 2021
    Location
    Albania
    Posts
    1
    Rep Power
    0

    Re: E2-01 error Daikin Altherma 3

    I have the same problem with the same device