    Unit is a RWEYQ72PCTJ with three AHUs and one BS Box. This was my first commission with a heat recovery Daikin and received a UF error. I suspect the system may be piped incorrectly and attached some layout diagrams. Anyone confirm?
    Also, I was able to count the number of AHUs and 3 were confirmed via the LEDs. When I entered the mode to count the BS Box, the LEDs showed 3 boxes when only one is installed. Very odd as HP7 should only be illuminated. Bug perhaps?
    Oct 2001
    Nottingham UK
    5,667
    Re: Daikin Piping Layout Confirmation and BS Box Count
    Error UF comes up as Indoor Unit failed to get address from Outdoor Unit.
    Sounds like a wiring issue rather than a piping issue.
    Feb 2015
    14
    When all of the equipment is turned on, Daikin finishes the addressing procedure when the HP2 LED goes out, right? I was able to initiate the first test run but it obviously failed.
    Oct 2001
    Nottingham UK
    5,667
    If the outdoor unit cannot 'handshake' the indoor unit then that is due to a lack of communication. This could be caused by a lack of power supply to the indoor unit, a fault in the F1 F2 wiring or failed indoor pcb.
    A piping error would show up when the initial 'Test' run is carried out.