    Mitsubishi City Multi disable IC and change capacity



    Hi,
    wondering if this is theoretically possible:

    Have a P200 outdoor unit that has a max indoor capacity of 300

    I wish to connect 2 groups each of 250 indoor units (total 500) but ONLY having one group available at a time.

    Questions:
    1) Does error 7100 (capacity error) Stop the system functioning or is it just a warning?

    2) Could I trick the outdoor unit by setting dip switches to that of a P350 giving a max capacity of P525

    3) remove the M-net's to those not in use while they're not being used?

    4) Something else?

    Thanks in advance!
    Last edited by WhosAce; 25-01-2021 at 08:29 PM.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Mitsubishi City Multi disable IC and change capacity

    How do you know that 50% of the gas charge is contained in each indoor group of 250 each time you isolate i group?

    could leave the other group under or over charged.

  3. #3
    Join Date
    Dec 2020
    Location
    uk
    Posts
    6
    Rep Power
    0

    Re: Mitsubishi City Multi disable IC and change capacity

    The pipe and other calcs are all within capacity spec for the P200 unit. I'm assuming the limit of 150% is due to most people expecting 100% capacity from all units simultaneously. I don't ever need that. The requirement is for 200-250 max

  4. #4
    Join Date
    Dec 2020
    Location
    uk
    Posts
    6
    Rep Power
    0

    Re: Mitsubishi City Multi disable IC and change capacity

    OK, changing the capacity on the outdoor unit causes an error and so does disabling the connected capacity setting. Time to get smart.

  5. #5
    Join Date
    Dec 2020
    Location
    uk
    Posts
    6
    Rep Power
    0

    Re: Mitsubishi City Multi disable IC and change capacity

    OK, cracked it I think! By disconnecting the M-net to a group of indoor units DURING outdoor unit start up it ignores the additional indoor units and all seems to operate normally.
    I will add a time circuit that disconnects the group via the M-net each time the outdoor unit starts up. Thanks for your help!