    LG problem



    Fitted my first (and last) LG floor standing split in december and a week later replaced the compressor under warranty due to the suction bend leaking.

    Worked fine, ran nearly 24/7 until today when it was not cooling or heating. Took the 200 screws out of the outdoor just to remove the cover, compressor was running but no heat coming from the discharge. Put gauges on every schreader, but each one was the same, reading the head pressure around 7 bar. (R22) Checked the resistance on the comp, all windings read the same. (3 phase)

    Any help much appreciated, I'm sure from reading a lot of threads theres a few engineers with LG experience!



  2. #2
    Join Date
    May 2006
    Location
    Leicestershire
    Age
    58
    Posts
    28
    Rep Power
    0

    Re: LG problem

    If the suction is reading the same as the head and the compressor is running then i'm afraid to say its a non pumper or the hot gas valve is stuck mid position.

  3. #3
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    62
    Posts
    588
    Rep Power
    19

    Re: LG problem

    Also dont forget if the fan speed board has been working intermittemtly before finally stopping, the internal presure releif valve blows off until it burns the comprosser out, I know...........I have been there!

    Is the compressor making a loud hissing noise?

  4. #4
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: LG problem

    Not making a hissing noise but seems a lot louder than it was at first.
    I dont think it could be the reversing valve bocked as the discharge pipe straight off the comp is only luke warm if that!

  5. #5
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: LG problem

    Turning the other way around. Did anybody reversed the phase sequence on the main breaker or distribution board between the installation and now?

  6. #6
    Join Date
    Mar 2006
    Location
    West Midlands
    Posts
    15
    Rep Power
    0

    Re: LG problem

    have had a few reverse valves passing on LG kit and it appears as if the compressor is not pumping so i would look at that option or as some else previously stated check for phase reversal as they are scrolls in those units but some models have got phase reversal protection. back to LG (Looks Good dont work etc,etc)

Similar Threads

  1. York Screw Oil Problem
    By tomt in forum Technical Discussions
    Replies: 10
    Last Post: 02-12-2009, 02:48 PM
  2. what's the problem
    By botrous in forum Air Conditioning
    Replies: 35
    Last Post: 22-06-2008, 02:54 AM
  3. Strange problem
    By Peter_1 in forum Electrical
    Replies: 9
    Last Post: 10-04-2007, 05:19 PM
  4. Condensation Problem At Door to Freezers
    By mmarch in forum Air Conditioning
    Replies: 5
    Last Post: 17-10-2005, 02:42 PM
  5. Problem with centrif - help requested
    By Brian_UK in forum Industrial Compressors
    Replies: 5
    Last Post: 03-08-2005, 10:31 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •