Results 1 to 2 of 2
  1. #1
    Join Date
    May 2013
    Location
    Portugal
    Posts
    2
    Rep Power
    0

    Panasonic H11 Error Code



    Hello,

    Hope you can help me with this problem.

    I have a CS-E9LKEW / CU-E9LKE air conditionig with H11 error code.

    Following the diagnosis method I disconnected terminal 3 wire and measure VDC between terminal 2 & 3 from the outdoor unit. It should be fluctuate between 20-70VDC.
    It is 42VDC not fluctuate.

    Then reconnect terminal 3 wire and measure VDC between terminal 2 & 3 from the outdoor unit. It should be fluctuate between 20-50VDC.
    It is 2.8VDC not fluctuate.

    Does someone had a similar problem?

    Thank you for all the help you can give me.

    Regards

    David Silva



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Panasonic H11 Error Code

    That sometimes depend on when you are making measurments, before or after error indication.
    Also it should be masured at DC voltage scale since AC is only carrier.

    At what multimeter position did you make your measurments?

    Disconect unit from power supply, and wait 10 min. Then connect your measuring instrument and recconect unit and check voltage at first 10-20 seconds.


    https://youtu.be/JPgoXH2h-9k
    Turn on captions!

    You can also make this simple communication tester!

    https://youtu.be/hlgbFkL6TOg
    Last edited by nike123; 10-01-2021 at 11:05 AM.