Thread: Daikin vrv e3 problem
-
09-01-2021, 04:18 PM #1
Daikin vrv e3 problem
Hi all, Daikin vrv 6hp, showing e3 error,gas not come out from the outdoor unit and compressor start up 2 amps suddenly it taken 15 amps, compressor heat up more.high and low pressure sensor replaced,eev replaced, compressor both new, HP &lp switch ok but still e3 error detected, some one know what is the problem, pls help
-
10-01-2021, 10:29 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Daikin vrv e3 problem
It looks like you have restriction in refrigerant flow from compressor. Reset the unit and confirm that you realy have too high pressure with measuring high pressure during compressor startup untill error is present again.
If not, and assuming you have OK sensors, then PCB is faulty.
Does error E3 is present in both cooling and heating mode?Last edited by nike123; 10-01-2021 at 10:31 AM.
-
10-01-2021, 01:25 PM #3
Re: Daikin vrv e3 problem
Yes sir, both side same problem , control pcb ok , Thx your support.
-
10-01-2021, 11:33 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Daikin vrv e3 problem
You did not confirmed that you actually measured high pressure.
-
11-01-2021, 04:42 AM #5
Re: Daikin vrv e3 problem
Hi ,I finally found its 4way valve defective,
fault rectify, thanks your response.