    Daikin vrv e3 problem



    Hi all, Daikin vrv 6hp, showing e3 error,gas not come out from the outdoor unit and compressor start up 2 amps suddenly it taken 15 amps, compressor heat up more.high and low pressure sensor replaced,eev replaced, compressor both new, HP &lp switch ok but still e3 error detected, some one know what is the problem, pls help



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Daikin vrv e3 problem

    It looks like you have restriction in refrigerant flow from compressor. Reset the unit and confirm that you realy have too high pressure with measuring high pressure during compressor startup untill error is present again.

    If not, and assuming you have OK sensors, then PCB is faulty.

    Does error E3 is present in both cooling and heating mode?
    Last edited by nike123; 10-01-2021 at 10:31 AM.

  3. #3
    Join Date
    Mar 2020
    Location
    India
    Posts
    13
    Rep Power
    0

    Re: Daikin vrv e3 problem

    Yes sir, both side same problem , control pcb ok , Thx your support.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Daikin vrv e3 problem

    You did not confirmed that you actually measured high pressure.

  5. #5
    Join Date
    Mar 2020
    Location
    India
    Posts
    13
    Rep Power
    0

    Re: Daikin vrv e3 problem

    Hi ,I finally found its 4way valve defective,
    fault rectify, thanks your response.