Results 1 to 10 of 10
    3,355
    Sabroe SMC 108LL MK4
    Anyone can offer advice on servicing this compressor.
    Has external oil filter, which is replaced if differential pressure high etc.
    In compressor sump is oil pump strainer 100um, is it cleanable, or throw away?
    Manual suggesting with LL (long life) 10-15000 hours before overhaul on ammonia duty.
    Any experiences?
    This is on small new system direct drive, VSD
    Oct 2016
    Serbia
    110
    8
    Re: Sabroe SMC 108LL MK4
    I made a lot of this. Every one with VSD.
    Do not wait high diff. pressure on oil filter.
    Change once a year , if need often.
    I usually change oil filter inside comp. on service "C".
    If comp. running in "NORMAL" condition -10,+35 or booster I made annual service once a year.
    Other service made every 10000 hours because its over 1500 rpm.
    This way "A","A","A","C".
    If you have HEATPUMP unit also every 10000 hours.
    But "A","B","A","C".
    I hope this help
    If you need some doc. please inform me.
    best regards
    AKI
    3,355
    Thanks AKI,
    Can you clarify when valve plates should be changed on LL if running 1460rpm
    Oct 2016
    Serbia
    110
    8
    I forget also change coalescer filter every 10000 hours , to reduce oil loose.
    3,355
    Quote Originally Posted by AKI View Post
    I hope this help
    best regards
    AKI
    AKI,
    Could you pass email on any documents on what ABC etc is.
    Any information on when to change valve plates , piston rings etc.
    Oct 2016
    Serbia
    110
    8
    RANGER1 in all of this sets A,B,C, always change ring plates.
    I send you doc. and part no. this sets.
    Oct 2016
    Serbia
    110
    8
    Also if you have VSD(like you sad" comp. running between 1500 and 1700 rpm, not 1460.
    regards
    AKI
    Oct 2016
    Serbia
    110
    8
    RANGER1 check email
    Oct 2016
    Serbia
    110
    8
    If you need part no. for this sets I will send you but not before monday.
    3,355
    AKI,
    Have part number thanks for help